I did a paper for the ASES annual conference proceedings, where it suggested from actual 8yr? data for Minnesota, that 3 day even 5 day periods of low sun were common every year,  but 7 to 10 days was rare, and longer than 15 days never occurred (in my data set).  A Phd thesis by J. Clink UofM has a similar result. 
Darryl  

--- On Wed, 12/2/09, Travis Creswell <tcreswell at ozarkenergyservices.com> wrote:

> From: Travis Creswell <tcreswell at ozarkenergyservices.com>
> Subject: Re: [RE-wrenches] Other's thoughts on Autonomy?
> To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
> Date: Wednesday, December 2, 2009, 1:35 PM
> 
> 
> 
>  
>  
> 
>  
> 
>  
> 
> 
> 
> 
> 
> 
> 
>  
> 
> 
> 
> Hi
> Joel, 
> 
> 
>   
> 
> I think we
> are all pretty much on the same
> page. 
> 
> 
>   
> 
> I’m
> speaking mainly about a full
> time off grid residence, commonly with flooded lead acid
> and of course a fossil
> back up generator. 
> 
> 
>   
> 
> Most of my
> full time off gridders don’t
> even need to their generator from late April to early
> October.  They report
> that it’s normal that by 10 or 11 am their CC is in
> float.  Then
> winter sets in with frequent 2-3 week periods of
> clouds.  Like Walt said,
> where is the magic cloudy day number for me?  Is it
> the average of 3 weeks
> of sun and 3 weeks of clouds for 1.5 weeks of
> autonomy?  That’s
> grossly oversized in the summer and still inadequate in the
> winter. 
> 
> 
>   
> 
> From my
> view, if you need xxx kWh’s
> per month to live that’s how many you need, and days
> of autonomy aren’t
> that meaningful when you can only generate 1/3rd
> of that with your
> array.  You have to run the generator just as many
> hours per month
> regardless of how many days of autonomy, right?  And I
> believe that if you
> factor in charge efficiency and self discharge the larger
> the bank has a few
> more hrs per month of generator usage. 
> 
> 
>   
> 
> Thanks for
> sharing your thoughts everyone. 
> 
> 
>   
> 
> Best,
> 
> 
> Travis
> Creswell 
> 
> Ozark
> Energy Services 
> 
> 
>   
> 
> 
> 
> 
> 
> 
> 
> 
> 
> From:
> re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Joel Davidson
> 
> Sent:
> Tuesday, December 01, 2009
> 6:38 PM
> 
> To:
> RE-wrenches
> 
> Subject: Re:
> [
>  RE-wrenches ] Other's thoughts on Autonomy?
> wasconcordbatteries, EQUALIZE Them! 
> 
> 
> 
>    
> 
> 
> 
> Hello
> Travis, 
> 
> 
> 
> 
> 
>   
> 
> 
> 
> 
> 
> I think that 2
> days is not enough battery autonomy in
> the Ozarks and many other locations unless you have a
> fossil fuel
> generator to carry you through long cloudy periods.
> Battery 
> autonomy is site and load specific. I've done systems
> with as little as 1
> day and as much as 3 weeks at 80% depth of discharge.
> Lately, I've been
> generically specing 1.5 days of autonomy at 50% d.o.d. to
> get the dialogue
> started with the customer. 
> 
> 
> 
> 
> 
>   
> 
> 
> 
> 
> 
> I use
> to spec up to 4 parallel strings of T-105s or
> L-16s in 2, 4, and 8 batteries in series, but now I keep
> the number of strings
> down to 3 or less and prefer 1 or 2 strings of
> big 2-volt cells to
> reduce the number of cells and
> connections. 
> 
> 
> 
> 
> 
>   
> 
> 
> 
> 
> 
> Southern
> California urban and
> suburban
> grid-tie PV systems are almost all non-battery although we
> still get asked
> about emergency power - until they hear how much it adds to
> the cost of a
> grid-tie PV system. 
> 
> 
> 
> 
> 
>   
> 
> 
> 
> 
> 
> Joel
> Davidson 
> 
> 
> 
> 
> 
> 
> 
> ----- Original
> Message -----  
> 
> 
> 
> 
> 
> From: Travis
> Creswell  
> 
> 
> 
> 
> 
> To: 'RE-wrenches'
>  
> 
> 
> 
> 
> 
> Sent: Tuesday,
> December
> 01, 2009 2:15 PM 
> 
> 
> 
> 
> 
> Subject: Re:
> [RE-wrenches]
> Other's thoughts on Autonomy? was concordbatteries,
> EQUALIZE Them! 
> 
> 
> 
> 
> 
>    
> 
> 
> 
> IMHO, one
> of the worst design
> boo-boo’s is going past more then 2 days of
> autonomy.  Personally, I
> no longer size much over one day because it’s my
> anecdotal observation that
> most batteries die of old age and being ignored long before
> cycles get
> them.  Speaking mostly about quality deep cycle
> flooded. 
> 
> 
>   
> 
> Lots of
> good things result; 
> 
> -50%-75%
> smaller battery bank means a
> $20,000 battery bank just turned into $5,000 bank which
> frees up a ton of money
> for more modules and now-a-days you can buy a lot more PV
> with that
> money.  More array mean far less reliance on
> autonomy.  I’ll
> take the trade all year long.  In the summer we have 3
> to 4 weeks of sun
> and one day of clouds and in the winter we get 3 to 4 week
> stretches with 1
> sunny day.  Autonomy doesn’t really matter in
> either case from what
> I’ve seen.  The larger the bank means more self
> discharge losses,
> which on large battery banks gets significant as they age.
>  5-15 years
> later you’ll still have all that array but no matter
> what you’re
> looking at new battery bank. 
> 
> 
>   
> 
> -If you
> study the quality deep cycle
> manufacturers literature you’ll see that you’ll
> see that anything
> over 1 day of autonomy is too much to allow the array to
> actually charge the
> battery bank anywhere near the recommended amps and just
> like rust, sulfation
> never sleeps. 
> 
> 
>   
> 
> -Less cells
> to water 
> 
> 
>   
> 
> -Less space
> required 
> 
> 
>   
> 
> -Given that
> a surprisingly high percentage
> of off gridders totally screw up on their first bank, no
> matter how much we all
> try we might as keep the stupid tax of replacing a 2.5 yr
> old battery bank to a
> minimum. 
> 
> 
>   
> 
> -All of
> this discussion about cross
> paralleling, buss bars, TLC with a gazillion connections
> and multiple strings
> goes away. 
> 
> 
>   
> 
> -And the
> best part is we don’t have
> to carry all of the lead into the basement and even better
> back out of the
> basement! 
> 
> 
>   
> 
> Just my
> .02.  Feel free to strongly
> disagree but let’s be polite about
> it. 
> 
> 
>   
> 
> Travis
> Creswell 
> 
> Ozark
> Energy Services 
> 
> 
>   
> 
> 
>   
> 
> 
>   
> 
> 
> 
> 
> 
> 
> 
> 
> 
> From:
> re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of R Ray Walters
> 
> Sent:
> Tuesday, December 01, 2009
> 12:44 PM
> 
> To:
> RE-wrenches
> 
> Subject: Re:
> [RE-wrenches] concord
> batteries, EQUALIZE Them! 
> 
> 
> 
>    
> 
>    
> 
> 
> 
> 
> 
> I
> used to think that
> one string was optimal; until I had a single cell failure
> take out an entire
> system for weeks. (try operating a 24 v system at 22v!
> ) 
> 
> 
> 
> 
> 
> I
> now think that 2
> parallel strings is optimum,  3 is OK, and 4 is
> max. 
> 
> 
> 
> 
> 
> At
> 4 parallel strings, we start spending more time looking to
> make sure all
> connectors are the same exact length etc. to insure equal
> operation. 
> 
> 
> 
> 
> 
> 
> 
> But of course how do you account for
> varying internal resistance of the
> batteries......?? 
> 
> 
> 
> 
> 
> 
> 
> I've done 4 parallel strings at 144
> DC of sealed batteries on an electric
> vehicle, but we were very careful with our resistances, I
> even switched to
> smaller wire, on closer strings, and calculated out the
> exact resistance, so
> all strings were theoretically equal. This set actually
> just died, but achieved
> its manufacturer's predicted cycle life. (B&B
> battery, 350 cycles to 80%
> DOD) 
> 
> 
> 
> 
> 
> So if you're careful, 4 strings can
> work well. 
> 
> 
> 
> 
> 
> Worst I've seen was 20 golf carts
> paralleled in a 12 v system, (10
> strings) and they didn't pull the main connections from
> across the set, just connected
> to one end. 
> 
> 
> 
> 
> 
> The results were very predictable, with
> the furthest batteries being
> chronically under charged, and the closest ones being over
> cycled to a
> premature death. 
> 
> 
> 
> 
> 
>    
> 
> 
> 
> 
> 
> Ray Walters 
> 
> 
> 
> 
> 
>    
> 
> 
> 
>    
> 
> 
> 
> 
> 
> On Dec 1, 2009, at 11:28 AM, Windsun at wind-sun.com
> wrote: 
> 
> 
> 
> 
>   
> 
>  
> 
> 
> 
> 
> 
> You gotta
> wonder about why the customer bought such a
> battery layout, or why the installer sold that kind of
> configuration (which
> ever it was) with so many small batteries. We would
> never recommend going
> over 2 parallel banks, but sometimes the "customer
> knows best...". 
> 
> 
> 
> 
> 
>   
> 
> 
> 
> 
> 
> 
> 
>    
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> 
> List sponsored by Home Power magazine
> 
> 
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> 
> 
> Options & settings:
> 
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> 
> 
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> 
> 
> List rules & etiquette:
> 
> www.re-wrenches.org/etiquette.htm
> 
> 
> 
> Check out participant bios:
> 
> www.members.re-wrenches.org 
> 
> 
> 
> 
> 
>  
> 
> 
> 
> -----Inline Attachment Follows-----
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 


      


More information about the RE-Wrenches mailing list