We added a T-240 transformer to step down voltage, 240 to 120 VAC into an
older system with a SW4024 this summer, and had input lead balancing issues
till OB had us pull the neutral from the generator to the x-former. This
cleared up some of the issue but not all of it. We even swapped out the
transformer and installed an OB X240 transformer and the issue persisted
identically, with and without the neutral from the generator to the
transformer hooked up.

OB, Koehler and myself are still trying to figure out the reason for this
unbalance. We are getting 22 amps /11amps on the 230VAC input to the
x-former. Switching the input leads does not change the unbalance.

Any thoughts out there?

Dana Orzel

Great Solar Works, Inc
www.solarwork.com
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076

I will be the shift in how the world uses power! - Dana Orzel


-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Larry Brown
Sent: Wednesday, November 11, 2009 11:27 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] generator

Allan,

Using a T-240 fed from the 30 amp twist lock, non GFI, outlet with  
240 volts and then taking the stepped down 120 volts into the Outback  
looks like it would solve the problem of having two neutral to ground  
bounds.
It is a little pricey for the extra T-240 needed but it means not  
altering the new generator and possibly voiding the warrantee.  It  
also leaves the 2-20 amp GFI receptacles on the generator in their  
proper working order for future use.

Thanks for the helpful fix

Larry

On Nov 10, 2009, at 8:10 PM, Allan Sindelar wrote:

> Larry,
> The single VFX3524 takes 19A plus loads from one leg, way  
> overloading that
> 120V leg. Your best bet would be to add a T240 or PSX240 to balance  
> both
> legs. Then use the 30A 240V receptacle on the Genereck. The twist-loc
> receptacle doesn't run through a GFI, so the tripping will go away.  
> Plus
> your VFX can overload and trip the 20A breaker when charging at the  
> full 19A
> and a surge load comes on. This would likely solve that.
>
> Contact me off-list if you'd like a pdf copy of the off-grid  
> gennies article
> in Home Power; it will help explain a bit about wiring with the !)$%&@
> bonded-chassis neutral and a few other issues.
>
>
> Allan Sindelar
> Allan at positiveenergysolar.com
> NABCEP Certified Photovoltaic Installer
> EE98J Journeyman Electrician
> Positive Energy, Inc.
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> 505 424-1112
> www.PositiveEnergySolar.com
>
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of  
> Larry Brown
> Sent: Tuesday, November 10, 2009 5:11 PM
> To: RE-wrenches
> Subject: [RE-wrenches] generator
>
> Fellow Wrenches,
>
> On an off the grid system we did for a client a year or two back, we
> installed an Outback VFX3524 mounted on a Midnight Solar E Panel.
> They had a manual pull Homelight generator as back up.  All worked  
> well.
> Recently the client upgraded to an electric start 8000 watt Generac
> generator.
> Now every time they start the new generator, the GFI 20 amp
> receptacle on the generator pops.
> There is probably a redundant neutral to ground bond that is causing
> this but I am uncertain on the best approach to remedy this condition
> Any recommendations or experience on how to get the generator to
> interface with the system?
>
> Thanks
> Larry
>
> Larry Brown
> Sun Mountain
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- 
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




More information about the RE-Wrenches mailing list