[RE-wrenches] OB Battery Charging

R Ray Walters ray at solarray.com
Sat Nov 7 18:53:34 EST 2009


I've been pretty happy with Outback's default settings. We use B&B  
sealed batteries and HUPs, and found that the same settings work for  
both. I haven't tried other sealed batteries which might need  
different settings. Rolls seemed to really need more absorption time,  
and higher voltage, and this is one reason we quit selling them.

R. Walters
ray at solarray.com
Solar Engineer




On Nov 7, 2009, at 1:49 PM, jay peltz wrote:

> HI Ray,
>
> What charge parameters are you using if you are not doing an EQ.
> volts absorb and volts float  and absorb time?
>
> thanks,
>
> jay
>
> peltz power
> On Nov 7, 2009, at 12:45 PM, R Ray Walters wrote:
>
>> I think that periodic Equalization is "old school", a concept left  
>> over from the days of C30 controllers that didn't fully charge the  
>> batteries on a regular basis.
>> I now only recommend Eq charging if:
>> a) the batteries have sat for over a month in a deeply discharged  
>> state, or
>> b) checking individual cell voltages indicates more than a 2%  
>> difference between batteries. (over a tenth on a 6 v battery)
>> Eqing every 30 days just isn't necessary with today's PWM temp  
>> compensated controllers IMHO.
>> Equalization charging can overheat batteries, which according to my  
>> research is the number one factor in reduced life.
>> Also, even when Eqing, I recommend the generator only be used to  
>> bring the batteries up to close to full charge, and then let the PV  
>> array perform the Equalization, thus the MATE isn't necessary.
>> I still do install MATEs on projects with owners that know what  
>> they're doing, and know when to equalize, etc.
>> Finally, its very inefficient to use a generator for the hours  
>> necessary for Equalization while running at fairly low power.
>> Hit the genie early in the morning, shut down most loads, and Eq  
>> with the array from 11:00am through the afternoon. If the array  
>> can't do this, then its undersized, or you have designed a highbred  
>> system that does require a MATE. (and an owner that understands  
>> what he's doing)
>>
>> R. Walters
>> ray at solarray.com
>> Solar Engineer
>>
>>
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20091107/99fddffb/attachment-0001.htm>


More information about the RE-Wrenches mailing list