No problem, so long as the insulation is rated for the highest
voltage conductor. Conductors of other systems (like premise wiring)
can not be in the raceway.
At 07:02 AM 9/24/2009, you wrote:
>Wrenchers,
>
>What's the deal with mixing AC and DC conductors in a raceway? The
>job in question has a 6x6 wireway under the inverters. Conductors
>will have their own conduits but is it ok for them to share the wireway?
>
>Thanks in advance for clarification on this,
>Nik
>
>
>--
>Nicholas Ponzio
>Building Energy
>1570 South Brownell Road
>Williston, VT 05495
>
>t: 802-859-3384 x15
>f: 802-658-3982
><http://www.BuildingEnergyVT.com>www.BuildingEnergyVT.com
>
>"Building Solutions for a Sustainable Future"
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
NABCEP TM Certified PV Installer
Office - 740-448-7328
Mobile - 740-856-9648
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090924/e03eb8cf/attachment-0001.htm>
More information about the RE-Wrenches
mailing list