[RE-wrenches] raintite box mounting angle

Darryl Thayer daryl_solar at yahoo.com
Wed Aug 26 19:19:21 EDT 2009


good point any conduit can carry moisture, and conduits from hot to cold can hve condensation, air flow should be avoided.  the duct seal is good for this
darryl

--- On Wed, 8/26/09, boB Gudgel <boB at midnitesolar.com> wrote:

> From: boB Gudgel <boB at midnitesolar.com>
> Subject: Re: [RE-wrenches] raintite box mounting angle
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Wednesday, August 26, 2009, 5:05 PM
> Conrad Geyser wrote:
> > 
> > We always fill any conduit at the point of building
> penetrations for air sealing. Otherwise in winter, not only
> will the conduit get house moisture condensing inside of it,
> but it will act a a nice thermo siphon for pulling warm air
> out of the house…..
> > 
> 
> Just a note here...
> 
> All six of the MidNite PV combiner boxes are rain "proof",
> but allow moisture to escape.
> 
> boB
> 
> 
> 
> 
> 
> 
> 
> 
> >
> ------------------------------------------------------------------------
> > 
> > *From:* re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> *On Behalf Of *Wind-sun.com
> > *Sent:* Tuesday, August 25, 2009 11:49 AM
> > *To:* jryago at netscape.com;
> RE-wrenches
> > *Subject:* Re: [RE-wrenches] raintite box mounting
> angle
> > 
> > It is almost impossible in a normal installation to
> get a totally waterproof enclosure.
> > 
> > What you describe with the flooded box is more common
> than people might think.
> > 
> > What causes most of that is condensation. Humid air
> gets sucked into the enclosure at night or whenever else it
> cools off. The water then condenses inside. Next day, the
> box heats up again and the air expands a bit again, but the
> water has already condensed and cannot get out.
> > 
> > That is why the weep hole as you noted is mandatory,
> especially in areas with high humidity. But we have seen
> this even in the desert regions of Arizona and CA, so it can
> happen anyplace over long periods of time.
> > 
> >
> ..................................................................................................
> > Northern Arizona Wind & Sun - Electricity >From
> The Sun Since 1979
> > Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
> >
> ..................................................................................................
> > 
> >     ----- Original Message -----
> > 
> >     *From:* Jeff Yago
> <mailto:jryago at netscape.com>
> > 
> >     *To:* kirk at vtsolar.com
> <mailto:kirk at vtsolar.com>
> ; RE-wrenches
> >     <mailto:re-wrenches at lists.re-wrenches.org>
> > 
> >     *Sent:* Tuesday, August 25,
> 2009 8:40 AM
> > 
> >     *Subject:* Re: [RE-wrenches]
> raintite box mounting angle
> > 
> > 
> >     I am getting more convinced
> that there is no such thing as a
> >     water-tight electrical
> enclosure, regardless of gasket covers and
> >     sealed openings. We always
> drill a very small "weep-hole" in the
> >     bottom of an enclosure. We
> have found this is too small to allow
> >     insects to enter, but will
> drain any leaks or moisture that gets
> >     condensed into a liquid. I was
> recently called by the owner of a
> >     large pole mounted array (that
> was installed by another firm )
> >     when the system stopped
> working and the originally installer was
> >     long gone. I absolutely swear
> to you that when I pulled the covers
> >     off several electrical
> junctions boxes, water POURED out of the
> >     enclosures! I am not talking
> about wet, I am saying about a quart
> >     of water was being held inside
> each enclosure by their water-proof
> >     gasketed covers. Needless to
> say, all of the electrical terminals
> >     and wire connectors inside
> these junction boxes were badly corroded.
> > 
> >     I know they make totally
> water-proof electrical equipment for
> >     under-water applications, but
> have found most outdoor rated
> >     electical enclosures will get
> some water inside and that includes
> >     under-ground conduit. Take
> some advice and regardless of mounting
> >     orientation, drill a small
> weep-hole in the bottom if there is not
> >     one provided by the
> manufacturer.
> > 
> >     Jeff Yago
> > 
> >     DTI Solar
> > 
> >
> ------------------------------------------------------------------------
> > 
> > _______________________________________________
> > List sponsored by Home Power magazine
> > 
> > List Address: RE-wrenches at lists.re-wrenches.org
> > 
> > Options & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> > 
> > List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> > 
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> > 
> > Check out participant bios:
> > www.members.re-wrenches.org
> > 
> >   
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 


      


More information about the RE-Wrenches mailing list