> are we talking about 2% voltage drop, resistance, or power loss?
No- I was talking about the 2% difference in resistance between two
wires, which is not the same thing as 2% voltage drop. What I got from
this discussion was that solid copper wire will help your voltage drop
by about 0.05%, a marginal benefit outweighed by the frustration of
exclusively using solid wire for wiring.
And sure, keeping losses low and not breaking wire strands at connectors
are important too. I did an inspection a few weeks ago where we opened
up the panelboard and the original contractor for the building had
broken off 3 strands from a #2/0 cable to fit it in the main lugs. Yikes!
DKC
-------- Original Message --------
Subject: [RE-wrenches] PV System Design Compromises (was solid vs
stranded AC vs DC)
From: Joel Davidson <joel.davidson at sbcglobal.net>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date: 2009/8/5 14:30
> Dave, I agree. but are we talking about 2% voltage drop, resistance, or
> power loss?
>
> What I got from this discussion about solid vs. stranded wire (1) use
> solid copper wire and (2) keep I2R losses low and (3) if you use
> stranded wire, be very diligent when tightening connectors. Anything else?
>
> Wrenches make design compromises every day. My 11 year old grid-tied
> system is an example:
> - Siemens SP70 modules because SP75s were unavailable.
> - Trace SW4048 at 65% efficiency because higher efficiency non-battery
> inverters were less reliable.
> - Low-rise, low-tilt angle array because Culver City did not allow PV
> arrays to be visible from the street.
> - And now, making improvements on a system that is working flawlessly
> for almost 100,000 hours does not make cost vs. benefits sense.
>
> Joel Davidson
>
>
> ----- Original Message ----- From: "Dave Click" <daveclick at fsec.ucf.edu>
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Sent: Wednesday, August 05, 2009 5:58 AM
> Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
>
>
>> 2% loss is significant, but I think that Darryl was saying that the
>> resistance for stranded wire was 2% higher than solid. So if you had a
>> 3% voltage drop in your system with stranded wire, you could rewire
>> the system with solid wire and have a voltage drop of (3% x 0.98)
>> 2.94% at peak production; that's less than 1 kWh/yr per kW installed.
>>
>> DKC
>>
>> -------- Original Message --------
>> Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
>> From: Joel Davidson <joel.davidson at sbcglobal.net>
>> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> Date: 2009/8/3 20:31
>>
>>> 2% loss from any resistance source over 25 years is significant.
>>>
>>> ----- Original Message ----- From: "Darryl Thayer"
>>> <daryl_solar at yahoo.com>
>>> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>>> Sent: Monday, August 03, 2009 2:04 PM
>>> Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
>>>
>>>
>>>
>>> Yes, that is what the code book and my electricians handbook says,
>>> but 2% is very little. I would think that passing through a conduit
>>> hole is larger than that.
>>> Darryl
>>>
>>> --- On Mon, 8/3/09, Matt Tritt <solarone at charter.net> wrote:
>>>
>>>> From: Matt Tritt <solarone at charter.net>
>>>> Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
>>>> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>>>> Date: Monday, August 3, 2009, 3:49 PM
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> Darryl,
>>>>
>>>>
>>>>
>>>> Say what?! This would seem to indicate that solid core is
>>>> actually
>>>> better for DC than stranded wire. Can this possibly be
>>>> true??
>>>>
>>>>
>>>>
>>>> Matt
>>>>
>>>>
>>>>
>>>> Darryl Thayer wrote:
>>>>
>>>> I looked in the code book and found stranded wire
>>>> has about 2% higher DC resistance than solid, Chapter 9
>>>> table 8, and that for AC resistance the same value as DC
>>>> resistance to within the table accuracy Chapter 9 Table 9
>>>>
>>>> This table points out that for AC resistance it is
>>>> important to know the conduit system, as the reactance will
>>>> have an effect. With AC it is important to never allow a
>>>> single wire to pass through a metal surface as this will
>>>> induce eddy currents and magnetic effects into the metal
>>>> causing voltage drop and heating.
>>>>
>>>> --- On Fri, 7/31/09, jay peltz <jay at asis.com>
>>>> wrote:
>>>>
>>>>
>>>>
>>>> From: jay peltz <jay at asis.com>
>>>> Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
>>>> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>>>> Date: Friday, July 31, 2009, 10:01 PM
>>>> Hi Darryl,
>>>>
>>>> But what are the differences and when do they come into
>>>> play?
>>>>
>>>>
>>>>
>>>>
>>>> On Jul 31, 2009, at 7:25 PM, Darryl Thayer wrote:
>>>>
>>>>
>>>>
>>>> Well there is very slight differences between AC
>>>> and
>>>>
>>>>
>>>> Dc But this
>>>>
>>>>
>>>> difference
>>>> is so slight that it has no effect on anything we will
>>>>
>>>>
>>>> do.
>>>>
>>>>
>>>> Darryl
>>>> --- On Fri, 7/31/09, jay peltz <jay at asis.com>
>>>>
>>>>
>>>> wrote:
>>>>
>>>>
>>>>
>>>> From: jay peltz <jay at asis.com>
>>>> Subject: [RE-wrenches] solid vs stranded AC
>>>>
>>>>
>>>>
>>>> vs DC
>>>>
>>>>
>>>>
>>>> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>>>> Date: Friday, July 31, 2009, 7:00 PM
>>>> HI All,
>>>>
>>>> I'm trying to understand this wire issue.
>>>>
>>>> Whether or not there is a difference between
>>>>
>>>>
>>>>
>>>> stranded or
>>>>
>>>>
>>>>
>>>> solid wire for DC or AC.
>>>>
>>>> Any takers on this one?
>>>>
>>>> thanks,
>>>>
>>>> jay
>>>>
>>>> peltz power
>>>> _______________________________________________
>>>> List sponsored by Home Power magazine
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Options & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Home Power magazine
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Options & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Home Power magazine
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Options & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Home Power magazine
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Options & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>>
>>>>
>>>>
>>>> No virus found in this incoming message.
>>>> Checked by AVG - www.avg.com
>>>> Version: 8.5.392 / Virus Database: 270.13.42/2279 - Release
>>>> Date: 08/03/09 05:57:00
>>>>
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> -----Inline Attachment Follows-----
>>>>
>>>> _______________________________________________
>>>> List sponsored by Home Power magazine
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Options & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive:
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive:
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list