[RE-wrenches] down-sizing main breaker
William Miller
william at millersolar.com
Sun Aug 2 11:33:49 EDT 2009
Allan:
At the point of the short circuit, the amperage will exceed the rating of a
100 amp feeder. If the main panel had no extra breaker spaces, it could
still be subject to a short circuit if, for example, a wrench is dropped
into it.
I should add that I am not an electrical engineer nor am I trying to
justify the codes that apply. I am just trying to explain how I see the
codes are applied. It is necessary to understand this to avoid incorrect
system design and fruitless discussions with building officials.
William
At 07:22 AM 8/2/2009, you wrote:
>William,
>Wow youre a master at whipping up drawings!
>
>OK, I get the concept, and its just as I described. The scenarios in
>drawings one and two are OK as long as both busbars are rated 150A
>(commercial) or 125A (residential.
>
>You then show that the reason for the upsized feeders is to handle a
>short. But wait! Even if the short could produce 140A, as you have
>indicated, the conductors will still not carry more than the 100A that
>theyre rated to carry. One would carry 100A from one panel and 40A from
>the other, Nowhere would that conductor carry 140A, and the mate to it
>would carry at most 60A. Increasing conductor size wouldnt change
>anything in that (or any) scenario. So why would you have to increase
>conductor size?
>
>Thanks, Allan
>
>----------
>From: re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
>Sent: Saturday, August 01, 2009 11:13 PM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] down-sizing main breaker
>
>Allan:
>
>I whipped up three drawings that indicate three overload scenarios
>possible with incorrectly sized distribution equipment. They are on our
>web site at: http://millersolar.com/case_studies/case_studies.html Click
>on Point of connection. Click on any drawing to see a larger version.
>
>I hope this helps with understanding the concept.
>
>William Miller