[RE-wrenches] down-sizing main breaker

Bill Brooks billbrooks7 at yahoo.com
Fri Jul 31 13:24:13 EDT 2009


Bruce,

 

Use a standard 125-amp panel with a 100-amp main breaker. This is a very
common panel and does not require downsizing the main breaker any further
(it is already downsized). It allows up to a 50-amp PV breaker.

 

Bill.

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mendocino
Solar Service
Sent: Friday, July 31, 2009 9:57 AM
To: RE-wrenches
Subject: [RE-wrenches] down-sizing main breaker

 

Hi Folks,

 

Can anyone provide code reference or advice on this question?

Our customer has 100 amp service at the meter pedestal, 100 amp main breaker
feeding 200 foot underground run to a 100 amp panel at the house. We need to
land a 40 amp breaker, so are proposing to replace main panel at house with
200 amp panel. The AHJ says we need a 200 amp main breaker in this panel,
which will work, but says this requires upsizing the feeder, main breaker at
meter, and therefore utility service to 200 amps.

 

I've read on this list and elsewhere about downsizing the main breaker in a
panel to create capacity to make the 120% rule. This AHJ says you can't put
in a breaker smaller than the panel size, and furthermore, everything
upstream would have to be upsized. Is this from the code?

Bruce Erickson

Mendocino Solar Service

PO Box 1252

Mendocino, CA 95460

707-937-1701

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090731/03853388/attachment-0001.htm>


More information about the RE-Wrenches mailing list