I have experienced the same thing with Outback and PVPowered.
DT
--- On Tue, 7/28/09, Mark Dickson <mark at oasismontana.com> wrote:
> From: Mark Dickson <mark at oasismontana.com>
> Subject: Re: [RE-wrenches] AC coupled with grid and backup generator
> To: jryago at netscape.com, "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
> Date: Tuesday, July 28, 2009, 12:40 PM
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> Jeff,
>
>
> I had this
> same hesitation when we first
> fired up our AC coupled system. When speaking with
> Steve at outback and he was
> pretty sure that the generator would put out dirty enough
> power that the
> Fronius inverter would not like it and shut down. He
> was correct—it goes into
> an error mode as soon as the geni kicks on. Once the
> generator shuts down the
> Fronius senses the frequency is back within range and
> resets itself. Turned
> out to be a simple solution and has been operating
> flawlessly for almost a year
> now.
>
>
>
>
> Good
> luck!
>
>
>
>
>
>
> Mark
> Dickson
>
> Oasis Montana
> Inc.
>
>
>
>
>
>
>
>
>
>
>
> From:
> re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> On Behalf Of
> Jeff Yago
>
> Sent:
> Tuesday, July 28, 2009 6:55
> AM
>
> To:
> RE-wrenches
>
> Subject: Re:
> [RE-wrenches] AC
> coupled with grid and backup generator
>
>
>
>
>
>
>
>
>
>
>
> We are completing a residential 4 kW solar system that is
> on the grid, but has
> backup battery-powered Xantrex 6 kW inverter, AC coupled
> Sunny-Boy inverter,
> and a 17 kW Kohler generator. The larger generator is
> to allow operation
> of a ground-source heat pump during winter which is not
> supplied from
> the inverter fed panel. We have added a relay
> cut-out for the Sunny
> Boy AC output to prevent over-charging the batteries during
> utility outage, but
> have some concerns about back-feeding the generator through
> the 100 amp 240 VAC
> transfer switch when the Sunny Boy thinks the grid is still
> up.
>
>
>
>
>
>
>
>
>
>
>
>
> Will the Sunny
> Boy try to couple to the generator like it
> will the inverter which will be feeding other house loads
> during an outage and
> if so, any risk? We have wired an aux.
> switch contact on the
> transfer switch to also lock out the Sunny Boy output using
> the same relay
> control as being used for high battery voltage cutout, but
> this is adding other
> issues related to needing multiple relays due to different
> relay coil voltages.
>
>
>
>
>
>
>
>
>
>
>
>
>
> Anyone smoked a
> large generator by back-feeding from
> inverter when the loads are reduced or shut
> off?
>
>
>
>
>
>
>
>
>
>
>
>
> Thanks,
>
>
>
>
>
>
>
>
>
>
>
>
>
> Jeff
> yago
>
>
>
>
>
>
>
>
>
>
>
>
>
> Netscape.
> Just the Net You Need.
>
>
>
>
>
>
>
>
>
>
> -----Inline Attachment Follows-----
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list