[RE-wrenches] Enphase comparison

Peter Parrish peter.parrish at calsolareng.com
Wed Jul 22 11:31:34 EDT 2009


We have installed EnPhase on two jobs in the 2-4 kW range and found that the
installation touch labor is about the same. The inverters install quickly on
ProSolar rails. You need to install the 240 VAC 2P switches on the roof, but
no big inverter on the ground. A wash IMHO.

 

They are great for mitigating the effects of shading.

 

- Peter

 


 

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com  
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885


 

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Marco
Mangelsdorf
Sent: Tuesday, July 21, 2009 9:31 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Enphase comparison

 

To those of you who have installed PV systems in, say, the 2-4 kW range
using Enphase inverters, how would you compare the labor time and
installation materials (wire, conduit, hardware, etc.)  to a standard system
design using a single inverter?

 

Longer?  Shorter?  More or less materials?  If either, by what percentage?

 

Thanks,

Marco

ProVision

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090722/e5752c18/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.gif
Type: image/gif
Size: 4274 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090722/e5752c18/attachment-0001.gif>


More information about the RE-Wrenches mailing list