[RE-wrenches] Inverter AM Interference
Tump
tump at hughes.net
Thu Jul 16 21:51:37 EDT 2009
I see that this install is using EMT, are you using a bonding bushings on
the EMT? If so, I had interference on a large PV powered refrigeration unit
that used an electronic expansion valve. The wires were installed inside EMT
causing all kinds of weird problems. When I removed bonding at both ends & I
bonded only one end, similar to when one connects the "drain" conductor on
"shielded w/ drain" cat 5 cable, This took care of the problem! Who knows
.....tump
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of boB Gudgel
Sent: Wednesday, July 15, 2009 8:12 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Inverter AM Interference
> SOLARPRO at aol.com wrote:
>
> This is a brand new 5000 US. EMT on all dc runs. The radio is a
> BOSE...and is 27 feet away. The interference is runs 24/7... so it
> must be AC related.
>
Does the radio noise go away when you completely disconnect the SMA
inverter ?
boB