[RE-wrenches] Roof Loading request for help

Chris Meier chrism at unirac.com
Fri Jul 10 15:28:44 EDT 2009


Wes you have a great point.

 

            Using PSF for a solar array can be a little misleading. With your example with 3.3 psf and a worse case down force wind load of 29 psf we exert a total of 32.3 psf on the 300 ft2 array for 9690lbs total, or 323lbs per attachment. This may not seem bad as basic 90 mph wind on 15 ft high building, but know put 4 or 5 attachments on the same structural member and now that member is carrying 1292 - 1615 lbs. This is not an evenly distributed load but multiple point loads. Will it crash a common house? No, but it does point out a distributed load can be miss leading. Using this lets say the installer spreads the attachment spacing out from 4' to 8'. The point load will double and if he does not stager the attachments from rail to rail the point loads will now be on less structural members increasing the member loads into 2584 - 3230lbs. All these options are still based on 3.3 psf array load at a 300 ft2 array. Now think of other point loads the building may have, HVAC and other mechanical equipment the closer we get to those the more we point loads can add up. 

 

As a general rule I do not worry much about this, but as you move into higher wind and snow loads this can really become an issue; even if the roof can handle the load using a PSF type rating, the point loads can be very surprising. The dead load of the array is normally not the primary concern. It is the live load of wind, dead load of snow and the array that can step up and get us in some rare circumstance. 

 

In my limited dealings with inspectors some seem to realize this so they want to see that the structure can handle these point loads. In other locations they seem to accept that if the loads are 500lbs or less then it will be ok, but go above this and they want engineering. Or they do not even care or think about it at all. 

 

I hope this makes sense.

 

Chris Meier

Residental Program Manager

UniRac, Inc.

1411 Broadway Blvd. NE

Albuquerque, NM   87102-1545

Ph:  505-242-6411 

Fx:  505-242-6412

Email:  chrism at unirac.com <mailto:chrism at unirac.com >  

Web:   http://www.unirac.com <http://www.unirac.com/> 

________________________________

From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of wes kennedy
Sent: Friday, July 10, 2009 11:45 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Roof Loading request for help

 

Hi All,

I am fully in favor of standardized permitting, and streamlining the process of installing PV.  With that said, I do think the "one layer of shingles = PV on roof thing" is apples and oranges.  Though the deadloading in psf is similar, PV doesn't sit on the roof, it lands on some sort of attachment, standoff, l-foot, what-have-you.

This leads to pretty high point loading values, doesn't it?  If you spread your 1000 lb array around 300 square feet, you get your 3.3 psf, BUT if it lands on 30 L feet, each of 4 square inches you end up with much higher points of concentrated loading.

Anybody worry  about that? 

Thanks!
Wes Kennedy
NABCEPian
   

--- On Tue, 7/7/09, Joel Davidson <joel.davidson at sbcglobal.net> wrote:


From: Joel Davidson <joel.davidson at sbcglobal.net>
Subject: Re: [RE-wrenches] Roof Loading request for help
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Tuesday, July 7, 2009, 7:13 PM

Allan,

In most of California (seismic zone 4) residential PV systems with solar arrays weighing less than 4 lb/ft2 do not require structural engineering if the roof has one layer of composition shingles. The reasoning is that roofs are allowed 2 layers of shingles (old set and re-roof set) and a layer of shingles weighs 4 lb/ft2 so 1 shingle layer and 1 solar array weighing less than 4 lb/ft2 is within the dead weight load limit. Hope this helps.

Joel Davidson

	----- Original Message ----- 

	From: Allan Sindelar 

	To: 'RE-wrenches' 

	Sent: Tuesday, July 07, 2009 5:26 PM

	Subject: [RE-wrenches] Roof Loading request for help

	 

	Wrenches,

	We are currently facing a city permitting bureaucracy that has recently discovered solar - that is, suddenly each department in the permitting and plan review departments is coming up with standards for PV systems. Some of the standards, of course, make no sense. 

	 

	PV systems typically add about three pounds per square foot to the loading on a roof. We are facing a city requirement for structural engineering work for standard roof attachment if the mounting approach is to make penetrations into the roof structure. This is a typical requirement that will only add considerable cost to each PV system, and we're looking to have our ammunition to fight this well stocked in advance. Specifically, are building authorities in other jurisdictions requiring structural engineering work for this type of roof attachment?

	 

	Thanks 

	Allan

	 

	Allan Sindelar

	Allan at positiveenergysolar.com

	NABCEP Certified Photovoltaic Installer

	EE98J Journeyman Electrician

	Positive Energy, Inc.

	3201 Calle Marie

	Santa Fe , New Mexico 87507

	505 424-1112

	www.positiveenergysolar.com <http://www.positiveenergysolar.com> 

	 

	
________________________________


	_______________________________________________
	List sponsored by Home Power magazine
	
	List Address: RE-wrenches at lists.re-wrenches.org
	
	Options & settings:
	http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
	
	List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
	
	List rules & etiquette:
	www.re-wrenches.org/etiquette.htm
	
	Check out participant bios:
	www.members.re-wrenches.org


-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org> 

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090710/8f39aab4/attachment-0001.htm>


More information about the RE-Wrenches mailing list