[RE-wrenches] xw xan buss cable lengths

Mark Edmunds mark.edmunds at xantrex.com
Thu Jul 9 12:55:11 EDT 2009


Hi Jay,

The "official" length limit is 130ft (40m), but we have lots of systems running at 200ft+ without problem. As long as the inverters and charge controllers are close together a long run to an SCP or AGS should be fine.

Cheers,

Mark


Mark Edmunds, P.Eng.
Senior Director Engineering 
New Product Development 
Xantrex Technology Inc. 
p. 604.422.2609 
f.  604.420.1591 
E-mail: mark.edmunds at xantrex.com 
Website: www.xantrex.com 


-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Thursday, July 09, 2009 8:41 AM
To: RE-wrenches
Subject: [RE-wrenches] xw xan buss cable lengths

Hi All,

Does anyone know the max cable length for the xanbus?