[RE-wrenches] Santa Monica guidlines/ CEC

Mark Frye markf at berkeleysolar.com
Thu Apr 23 09:34:49 EDT 2009


Nick,
 
It looks like the inspector is saying that he is refering to NEC 2005 by way
of CEC 2007 and mostly concerned about identifing wires of differant systems
by using different colors or other means.
 
His first line seems to be abbreviated or confused. He may be confusing the
PV output circuit with the inverter output circuits or just leaving that
part out.  Of couse the DC of the PV source and output circuits can be in
the same raceway with each other. But what if you want to add the AC of the
"inverter output "circuits in that same raceway?  This is allowed but you
have identify the conductors of the different systems.  So you can't have
black wire for the DC pos and then use black wire for the AC lines.  And
remember no tapping wire smaller #6.
 
If you look at it in these terms does does it become more clear what he is
getting at?
 
Mark Frye 
Berkeley Solar Electric Systems 
303 Redbud Way 
Nevada City,  CA 95959 
(530) 401-8024 
 <http://www.berkeleysolar.com/> www.berkeleysolar.com  
 

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Nick Vida
Sent: Wednesday, April 22, 2009 10:04 PM
To: re-wrenches at lists.re-wrenches.org
Cc: nickvida at ymail.com
Subject: [RE-wrenches] Santa Monica guidlines/ CEC


Wrenches,

This is an interesting email i received today from an inspector in Santa
Monica, CA. He reference the CEC, and I am not familiar. Is this the
Canadian Electrical Code(CEC)? 

Also, 
Santa Monica, CA just published their guidelines and there is a link in the
email. They are pretty close to the one Bil Brooks worked on for
Schwarzenegger. 


  _____  


Here is the Email (my draft of my response follows):

Hi Nick

It is my understanding that your permit will be extended by 6 months.

Here is the short cut for the SM PV standards.

Shortcut to:
http://www.qcode.us/codes/
<http://www.qcode.us/codes/santamonica/index.php?topic=8-8_40>
santamonica/index.php?topic=8-8_40

Weather and sunlight resistant stickers are acceptable.


The following correction items are in commonly overlooked.
*       The PV source and PV output circuits can not be contained in the
same raceways per 690.4(B).
*       A newer and commonly missed requirement is the identification of
conductors of different systems. The conductors of the DC are required
to be identified differently per 2007 CEC 310.12, 215.12, 210.5(C) and
200.6. The 2007 CEC is based on the 2005 NEC.
*       Please download the CalOSHA requirements for the installation of
ladders.  Inspectors will not climb ladders that are not compliant with
the requirements.  Please be prepared to install a suitable ladder,
inspectors may not be permitted adequate time to wait for the
installation of various ladders.

If I can be of further help please don't hesitate to contact me.  Thanks


Nick Katsenis
Combination Building Inspector
1685 Main Street
Santa Monica, CA 90401

310.458.2201 ext.8120
310.458.2104 Fax
nicholas.katsenis at smgov.net


  _____  


my response draft is:

Nick-

The following correction items are in commonly overlooked.
> *       The PV source and PV output circuits can not be contained in the
> same raceways per 690.4(B).

the rest of the sentence you are referencing is:

"as feeder or branch circuits of other systems..."

The clarification note in the handbook is:

For example, 690.4(B) does not permit the conductors supplying an exterior
lighting fixture located in close proximity of a roof- mounted PV array to
be installed in the same raceway or cable with the conductors of PV source
circuits or PV output circuits.
Conductores directly related to a specific PV system, such as those in dc
and ac output power circuits, may be contained in the same raceway as PV
source and output conductors... (page 1020 2005 NEC Handbook)

We would only be running the solar circuits in our raceways connecting
different runs to our gear. Are you saying you have a concern about such a
raceway?