[RE-wrenches] Solar vent for flat roof
Joel Davidson
joel.davidson at sbcglobal.net
Wed Apr 8 21:23:08 EDT 2009
The room has adequate passive ventilation. The roof vent is needed just to actively increase the air flow. The Solatube vent should do the job unless someone can suggest something better.Thank you all for your help.
Best regards,
Joel Davidson
----- Original Message -----
From: Kent Osterberg
To: RE-wrenches
Sent: Wednesday, April 08, 2009 12:59 PM
Subject: Re: [RE-wrenches] Solar vent for flat roof
Allan,
I recently studied this battery room venting issue when an inspector challenged me to show that a Zephyr vent was adequate to vent a room with a 48-volt 1700-amphour battery bank. I ended up finding that to keep the hydrogen concentration down to 1% (1/4 the explosive limit) required 75 CFM. The Zephyr vent at 5 CFM wasn't anywhere near sufficient; we ended up putting in a 100 CFM vent fan that is activated when the battery voltage exceeds 2.4 volts/cell.
Using a solar vent fan is probably a good solution as long as the only charging source is solar. If there are any other charging sources, a solar vent fan wouldn't be adequate.
Kent Osterberg
Blue Mountain Solar
Allan Sindelar wrote:
We have twice used pairs of Zephyr Power Vents to successfully vent large
banks, up to around 2200A/hr @48V. A 12V unit exits roof or wall with a 2"
pvc stack; 48V is 3"; thus they flash just like standard plumbing vents.
Note that the charge rate is more important than battery capacity, as it
determines the amount of gassing that must be exhausted.
Allan at Positive Energy
-----Original Message-----
Wrenches,
Our client has 48 IBE 85N-15 batteries in a room with a flat roof. What is
your recommendation for a solar powered vent that works well and flashes
well so that it does not leak? Thanks in advance for your advice.
Joel Davidson
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
----------------------------------------------------------------------------
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 8.0.238 / Virus Database: 270.11.45/2045 - Release Date: 04/07/09 06:41:00
------------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090408/1c870c3b/attachment-0001.htm>
More information about the RE-Wrenches
mailing list