Daryl:
This seems like a natural application would be for solar water pumping when
the head and flow requirements take you way above the standard 2 to 3 HP
"solar" pump sizes. Sounds like you are using the VFD to replace the
controller on the smaller solar pumping systems.
Would this work with PV only? (no generator, no grid, no batteries....??)
Thanks,
Walt Ratterman
SunEnergy Power
www.sunepi.org
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Darryl
Thayer
Sent: Friday, March 13, 2009 1:58 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] grid tie sync with big stiff genny?
HI All
This system is very large and is out of my experience range. BUT I have
seamlessly integrated a 40 HP motor and a grid/generator/solar tie. We also
do a related lab experiment in my solar class. Voltages may make these
methods prohibitive in your case prohibitive in your case. This is a little
bit outside of the box so read carefully.
Your load is mostly motors, probably with a much much smaller need for
120/208 lighting and plug loads (perhaps less than one percent).
Motors and particular pumps for a water system are on speed drives for
reasons of control and energy savings. These speed drives have DC busses
that operate from AC power sources and drive AC motors.
DC coupled solar gen set
The DC from the solar array can be feed directly into a VFD "speed drive's"
DC buss. In our lab experiment the students connect the solar array
directly into a 10 hp VFD, and 3 phase motors are driven from the speed
drive. The array voltage must be in range of the allowed VFD bus voltage,
the speed drive will stop drawing AC as the array provides all the power,
current, and share current as the array power drops. The problem is of
course you do not have MPPT on the array. The second approach is to use an
inverter from the Array and boost the voltage above 10% or so above the AC
voltage of the AC mains and rectify the this to power the DC bus of the VFD.
Caution the non-linier load of the rectifier may overload the inverter.
I have done the first suggestion, but not the second.
DT
--- On Thu, 3/12/09, Drake Chamberlin <drake.chamberlin at redwoodalliance.org>
wrote:
> From: Drake Chamberlin <drake.chamberlin at redwoodalliance.org>
> Subject: Re: [RE-wrenches] grid tie sync with big stiff genny?
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Thursday, March 12, 2009, 9:40 PM
> This should be possible. I have discussed what it might
> take to set
> up a system like that in the Gambia, with wind generators.
> It would
> take a control system with differential current sensors and
> other
> features. The UL 1741 specifications would probably need
> to be
> opened up on multiple direct grid tie inverters. There
> would be a
> practical limit on the percentage of feed to the generator
> mini grid.
>
> This being said, I've not received much encouragement
> with this
> idea. There are a lot of factors to consider.
>
>
> At 09:35 AM 3/11/2009, you wrote:
>
> >Undoubtably many of us are getting interesting project
> requests as
> >folks want to sprinkle magic stimulus dust on things to
> make solar
> >panels grow...
> >
> >
> >
> >We have a project with a huge electrical load, pumping
> water for a
> >medium sized city. They want solar... great. Easy.
> >
> >
> >
> >They had a power outage and kept running with 2.6 MW of
> diesel
> >generators. They are interested in solar's ability
> to do
> >"backup". I don't think that many
> batteries will fit in my pickup
> >truck, and I hate working with 300/0 wire.
> >
> >
> >
> >QUESTION: (and maybe its an easy one and the SMA guys
> will say,
> >sure, we did that in Greece). Is it viable to set up a
> micro-grid
> >in this scenario and run an island-mode, with available
> solar
> >reducing the genny plant demand? Should I just say
> "forget it" or,
> >at this MW scale, would the switchgear and effort be
> practical?
> >
> >
> >
> >Thanks.
> >
> >For a brighter energy future,
> >
> >Geoff Greenfield
> >President
> >Third Sun Solar & Wind Power Ltd.
> >340 West State Street, Unit 25
> >Athens, OH 45701
> >
> >740.597.3111 Fax 740.597.1548
> >www.Third-Sun.com
> >
> >Clean Energy - Expertly Installed
> >
> >
> >_______________________________________________
> >List sponsored by Home Power magazine
> >
> >List Address: RE-wrenches at lists.re-wrenches.org
> >
> >Options & settings:
> >http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> >List-Archive:
> >http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> >List rules & etiquette:
> >www.re-wrenches.org/etiquette.htm
> >
> >Check out participant bios:
> >www.members.re-wrenches.org
>
> Drake Chamberlin
> Athens Electric
> OH License 44810
> CO License 3773
> 740-448-7328
> 740-856-9648
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
__________ Information from ESET NOD32 Antivirus, version of virus signature
database 3935 (20090313) __________
The message was checked by ESET NOD32 Antivirus.
http://www.eset.com
More information about the RE-Wrenches
mailing list