[RE-wrenches] grid tie sync with big stiff genny?

Mark Edmunds mark.edmunds at xantrex.com
Fri Mar 13 17:22:40 EDT 2009


Hi Drake - the limit in the PV in this case was so we could not exceed
the minimum load in the subdivision, to make sure there was no back feed
to the generator.

Mark



Mark Edmunds, P.Eng.
Director Engineering 
Residential Renewable Energy Markets 
Xantrex Technology Inc. 

E-mail: mark.edmunds at xantrex.com 
Website: www.xantrex.com 



-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Drake
Chamberlin
Sent: Friday, March 13, 2009 1:47 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] grid tie sync with big stiff genny?

Hi Mark,

That looks like a great installation.  Is the max that can be fed 
into a generator mini grid 15%?

Since the system was able to keep the UL 1741 settings, that means 
this setup could feed both a utility grid and a generator mini grid, 
using the system transfer switch.

At 11:34 AM 3/13/2009, you wrote:

>We did a test installation in northern British Columbia with 28kW of 
>PV and GT5 inverters selling to a 90kW Genny system in a remote 
>off-grid community. So far we have just stuck to the normal 1741 
>islanding settings, and the system has been working smoothly. The PV 
>was basically sized so that it would not exceed the lowest mid-day 
>load on the small grid, and there was already an automatic dump load 
>in the system to ensure the diesels never became completely unloaded.
>
>
>
>So far the system has been working very well, with good fuel saving 
>for the community. You can read more about it here.
>
>




More information about the RE-Wrenches mailing list