Hi Drake,

Dont know why not. Meet code as much as possible:

1) AWG of the lightning down conductor adequate?
2) Use non reversible, listed connector to splice array SGEC
    to down conductor
3) Do you need an additional ground rod? Resistance to earth OK?
4) These rod/rods need to be bonded to the structure grounding electrode system
5) Is there an AHJ? If so, ask for input.

Hope this helps.

Dick

Dick Ratico
Solarwind Electric


--- You wrote:
Can the supplemental grounding electrode conductor be connected to a 
lightning protection system?

We have a case where it would be difficult to run a GEC down a multi 
story building, but have a convenient copper wire, from a lightning 
protection system, that runs to a rod.

Thank you,

Drake Chamberlin
Athens Electric
OH License 44810
CO License 3773
740-448-7328
740-856-9648  
--- end of quote ---