[RE-wrenches] Point of connection
William Miller
william at millersolar.com
Mon Feb 9 20:52:14 EST 2009
Keith:
No matter how you slice it, every breaker panel and every conductor in the
feeder from the inverter to the meter must meet the 120% rule. You can not
dedicate one panel as an "AC Combiner" and exceed the 120% rating on that
panel only. It does not matter if the source is one inverter or 10
inverters. You either meet the 120% requirement from section (B) or you
supply a supply side tap as allowed in (A).
William Miller
At 02:40 PM 2/9/2009, you wrote:
>Hello
>
>With the growth of the solar industry coupled with the generous incentives
>now offered on fed part of the equation, we are seeing some trends here
>and wondering what the approach has been in other areas. What kind of
>feedback are you receiving from the AHJ?
>
>There are some integrators who now are installing "systems" meaning,
>multiple small inverters that are married to smaller arrays as opposed to
>one large array with one large inverter.
>
>So, it is quite conceivable to have, for example, 3- 3000 W SMA inverters
>on a customers home. So, the point of connection issues arise. When you
>look at 690.64B, it speaks to the 120% of the busbar rating.
>
>What are folks doing in other areas, for this above example to address the
>mechanical/electrical challenges associated with this situation, when if
>you had 1- 200 amp residential service? There is alot of discussion, like
>installing a 125 amp rated subpanel; interuppting the feeder from the
>electric service and installing a 225 amp panel with a higher rated buss
>(hard to find or custom made thru Cutler Hammer or others) etc.
>
>We can also see a trend using the enphase products as well, but not as
>much pronounced. It could be conceivable for a client to want to build
>their system up over a few years and have 15, 175 watt panels on a circuit
>(2P15 amp) and grow the system up to lets say, 45, 175 watt panels (3-2P15
>amp). Same situation, different inverter manufacturer. My sense is this
>trend will continue for the forseeable future, and alot of wrenches will
>find orphaned systems out there and we should look at ways to address
>point of connection issues that are bound to present themselves.
>
>Thanks
>
>Keith
Please note new e-mail address and domain:
William Miller
Miller Solar
Voice :805-438-5600 Fax: 805-438-4607
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090209/0bfff060/attachment-0001.htm>
More information about the RE-Wrenches
mailing list