We use ANL type fuses (see here) in mobile applications for circuits  
like converters, generator starters and other heavy distribution  
circuits up to 300 amp. For large inverters with 2/0 and above cable  
we recommend Class T fusing.

The Prosine 1000 should be protected with a 150 amp fuse (see table 4  
of the manual). For simple short circuit protection the ANL should  
work fine. It has an interrupt rating of about 2700 amperes and up to  
80 Vdc. I am not positive about the legality. The way I understand it,  
SAE makes standards and NEC makes no rules for 12 volt mobile systems.

Larry Crutcher
Starlight Solar
11279 S. Glenwood Ave #11114
Yuma, AZ 85367
(928) 941-1660

larry at starlightsolar.com
www.starlightsolar.com

Retail Store: 2998 Shari, Yuma, AZ

Renewable Energy Products, Service and Installation





On Jan 19, 2009, at 9:49 AM, Peter Parrish wrote:

> We are designing a "Mobile Solar Power Center" to power Eco-Events  
> and the
> like in Southern California. We will have 1,600 Wp of solar panels,  
> 6 kWh of
> 24 V AGM battery backup and a 1kW / 120 VAC inverter. I am designing  
> the
> system from scratch, and I wondered if anyone else out there has put
> together a similar system and was inclined to share notes. When I'm  
> finished
> I'd be glad to do the same.
>
> One stumbling block I have right now, is to find a DC rated 70A in- 
> line
> fuse, to put between the battery bank and the input to the inverter.  
> 70A may
> seem an odd value, but it is the best choice for the surge rating of  
> the
> inverter I'll be using (Xantrex Prosine 1000). Does anyone have a  
> source for
> DC-rated in-line fuses?
>
> Thanks in advance, -Peter
>
> Peter T. Parrish, President
> California Solar Engineering, Inc.
> 820 Cynthia Ave., Los Angeles, CA 90065
> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
> CA Lic. 854779, NABCEP Cert. 031806-26
> peter.parrish at calsolareng.com
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090119/d10fb1a6/attachment-0001.htm>


More information about the RE-Wrenches mailing list