Colleagues:
I have a good friend that is a licensed electrical engineer. I forwarded
to him the background about the Yorba Linda certification
requirement. Below is his response, which I think is very pertinent to
this list. I redacted his name and contact information because I forgot to
ask his permission to post his response to the list. If anyone wishes to
pose any questions, I can forward.
With any PV system in the field, there are several variables which are
difficult to quantify: Insolation, both instantaneous and over time,
temperature at the module, and wind speed. When I am looking at a PV
system to evaluate suitable operation, there is some subjectivity in
determining acceptable output. I believe it would be difficult to give a go
or no-go determination to a given system. As my friend asks below, "who
sets the standards, and what are they?"
William Miller
>Generally problems in this area come down to legal definitions. You used
>the word "commission", they use the words "test and approve". Some of
>these words have legal meanings that assign risk and liability. This is a
>common misconception. Engineers design systems and set the parameters that
>constitute the performance metrics of that system. Like the men and women
>at Siemens or Square D. Once these metrics are established, they can be
>used by qualified installers and technicians as benchmarks in the field to
>determine if the system is performing as designed. So first off, you do
>not need an engineer to perform tests: The performance parameters are
>published, the inspector witnesses a field test by the installing
>contractor or testing agency technician that demonstrates the parameters
>are met and you're done. Second, most engineers have little or no actual
>experience field testing electrical equipment. Many wouldn't even know
>what a megger is or how to use it. A trained technician is typically far
>better trained and equipped to perform this task. There are good size
>companies such as ElectroTest that do this stuff exclusively and there
>isn't an engineer in the bunch (except in their offices). Finally, the
>main reason to use a registered engineer is to protect the public
>concerning life safety issues and so you can assign professional
>liability. That is why the state requires the license and insurance. My
>professional liability policy specifically limits any testing and
>"approval" activities I perform. They typically will not cover any of it.
>Only systems I design and even then there is a limit of liability
>concerning the manufactured equipment (tested and listed by others) used
>within the system. Which is why I said a registered engineer would be
>foolish to do this. So if the City thinks they are getting something (such
>as professional responsibility) by requiring this, they are misinformed
>and I am serious when I recommend they call the state board and ask them
>about this requirement. I am sure the board will dissuade them from this.
>As far as a business model, I would think a specialty contractor would be
>the best for this. But really it begs the question: What is it they are
>thinking you are going to test? Voltage? Output? Grounding safety? Who is
>publishing testing guidelines that someone can use to constitute an
>"approved" installation? It is just half baked bureaucratic psychobabble
>and should be challenged as such. That is my two cents. J
>
>
>G__:
>
>I am curious about you response. What problems do you see with a
>registered engineer commissioning a grid-tie system. The consensus is
>that there is little to test with one of these systems. A voltmeter,
>ammeter, insolation meter and maybe a megger are all that are required.
>
>William
>
>
>
>At 03:14 PM 12/21/2009, you wrote:
>
>Incredible. What "registered engineer" would be foolish enough to "test
>and approve" something like this? I would recommend the city of Yorba
>Linda call the state board and ask them what they think of this statement.
>It is patently misguided.
>
>G___ N___
>
>
>From: William Miller
>[<mailto:william at millersolar.com>mailto:william at millersolar.com]
>Sent: Friday, December 18, 2009 3:09 PM
>To: g___
>Subject: Fwd: [RE-wrenches] Solar System Certification
>
>G___:
>
>The posting below is from an industry chat list. I though you might find
>it interesting.
>
>The ordinance can be found
>at:
><http://www.municode.com/resources/gateway.asp?pid=13406&sid=5>http://www.municode.com/resources/gateway.asp?pid=13406&sid=5
>This requirement is not a bad idea. It would drive up the cost of PV, but
>it would protect consumers. Would be a good line of work for someone with
>your credentials.
>
>William
>
>
>
>
>I am curious if any of you have had to deal with this issue before.
>
>The following is an item we got back from the City of Yorba Linda for a
>Plan Check correction:
>
>
> All electrical solar systems shall be tested and approved by a
> California Registered Electrical Engineer. The engineer shall furnish a
> report stating their name, registration number, its date of expiration,
> address where the testing occurred and the dates of testing and
> approval. Such report shall be presented to the City inspector for
> approval at the time of final inspection. (YLMC 15.28.020) Note on the plans.
>
>All experiences and suggestion are appreciated.
>
>
>
>Best Regards,
>Brian C. White
>Design Engineer - PV Systems
>
>Eagle Roofing Products
>120 North Auburn Street - Suite 212
>Grass Valley, CA 95945
>Phone: 530-273-2948
>Cell: 530-575-5550
>e-mail: brianw at eagleroofing.com