[RE-wrenches] DC disconnect placement
Richard L Ratico
Richard.L.Ratico at VALLEY.NET
Sun Dec 20 14:34:26 EST 2009
William,
Not sure I understand how buried PV runs protected by touchsafe fuses in
combiner boxes at the array and GFCI protection at the inverters constitute a
fire hazard.
That's not saying I disagree with your disconnect here. I don't. If it was a 1kW
system, would you still install one? I would not.
Would not a deeper trench with properly located burial tape have been a good
call? If the array was installed and visible, maybe the excavation operator
would have thought to ask about underground utilities.
They should have anyway. Would not common sense imply the operator would drop a
bucket of fill on any sign of arcing. Would they know to look for a disconnect
at the array in any case?
Common sense can be slippery.
Dick
Solarwind Electric
--- You wrote:
Friends:
I am embarking on a 10 Kw ground mount grid-tie installation. The client
prepared for this installation some time ago by stubbing a PVC conduit
underground towards the future location of the PV array. Prior to
beginning this job, an excavation contractor intercepted the empty conduit
with a backhoe.
No harm was done because this conduit was empty. Had this conduit been
filled with PV feeders, it would have been very necessary to be able to
disconnect the PV arrays, both for safety and to prevent a brush fire in
our very dry climate.
The inverters will be located in a pump house about 130 feet from the PV
arrays. I would not normally put disconnects at the array and they are not
required. This scenario, however, has caused me to reconsider. The design
now calls for a disconnect at each row of modules. I feel that it would
not be prudent to delete this important safety item.
I wish there were a better selection of compact, low profile disconnects
suitable for a roof-top installation. I have put external handle
disconnects on roof but they look terrible. I may specify touch-safe fuse
holders inside of a Sola Deck for future comp roof jobs. I am not sure
what we will do with tile roofs.
It seems to me that every source of power should have a means of
disconnection as close to the source as possible. This is just common sense.
William Miller
Please note new e-mail address and domain:
William Miller
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
--- end of quote ---
More information about the RE-Wrenches
mailing list