[RE-wrenches] Off-Grid Sizing Case
Darryl Thayer
daryl_solar at yahoo.com
Thu Dec 10 09:29:03 EST 2009
The system is way short on PV, and I would think that it is already a Gen with PV support. I agree with everybody more PV is the way to go but the batteries must be cooked by now with this many Deep cycles. BTW C/10 is not important, in fact I feel better if I charge slower. I know fast charging is a good way to kill batteries. Operating cost needs a high efficiency engine. So until you can get the PV up to become the dominant source, a gen is probibly in order. I tend to use smaller generators than most people, and the fuel efficency of a Honda inverter gen is hard to beat.
--- On Thu, 12/3/09, Windsun at wind-sun.com <windsun at wind-sun.com> wrote:
> From: Windsun at wind-sun.com <windsun at wind-sun.com>
> Subject: Re: [RE-wrenches] Off-Grid Sizing Case
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Thursday, December 3, 2009, 12:18 PM
>
> Off-Grid Sizing Case
>
>
>
>
>
> The rate of charging is not the
> real problem in most
> undersized systems, it is the fact that the batteries
> seldom, if ever, get fully
> charged. Given the ratio of PV vs battery capacity, I would
> suspect that their
> batteries have been chronically undercharged for ages. We
> usually recommend
> around 1 watt of pv per AH for a 12 volt system, 2
> watts for 24 volt
> etc.
>
> A generator is not usually the
> answer, because it may
> have to run for hours to get that final 5-15% of charge
> into the batteries.
> Generators are good for equalizing, not so much for general
>
> charging.
>
> ..................................................................................................
> Northern
> Arizona Wind & Sun - Electricity From The Sun Since
> 1979
> Solar Discussion
> Forum: http://www.wind-sun.com/ForumVB/
> ..................................................................................................
>
> ----- Original Message
> -----
> From:
> Mark
> Frye
> To: 'RE-wrenches'
>
> Sent: Thursday,
> December 03, 2009 10:56
> AM
> Subject: Re:
> [RE-wrenches] Off-Grid
> Sizing Case
>
>
> So being able to achieve C10
> charging from the PV is not so
> important?
>
> Mark
> Frye
> Berkeley Solar
> Electric
> Systems
> 303 Redbud
> Way
> Nevada
> City, CA 95959
> (530) 401-8024
> www.berkeleysolar.com
>
>
>
>
> From: re-wrenches-bounces at lists.re-wrenches.org
>
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of Windsun at wind-sun.com
> Sent:
> Thursday, December 03, 2009 9:51 AM
> To:
> RE-wrenches
> Subject: Re: [RE-wrenches] Off-Grid Sizing
> Case
>
>
>
> I would go with #1.
> The solar is obviously
> undersized for the battery bank he has. Another panel +
> MPPT should give him
> about 25-40% more, depending on temps etc.
>
>
> ..................................................................................................
> Northern
> Arizona Wind & Sun - Electricity From The Sun Since
> 1979
> Solar
> Discussion Forum: http://www.wind-sun.com/ForumVB/
> ..................................................................................................
>
>
>
> _______________________________________________
> List sponsored by
> Home Power magazine
>
> List Address:
> RE-wrenches at lists.re-wrenches.org
>
> Options &
> settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
>
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List
> rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out
> participant
> bios:
> www.members.re-wrenches.org
>
>
>
> -----Inline Attachment Follows-----
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list