[RE-wrenches] Strings and series of batteries

Tump tump at hughes.net
Wed Dec 2 07:32:45 EST 2009


Surrette Battery, THE battery company suggests NO MORE the 3 parallel in a
string & would like to see 2 preferably.
If there are more the 3 then they really not interested in warrantee issues.
Jamie where are you??????
 
Now a days there are plenty of options for a good size/AH BB that can be
configured in 1 or 2 parallel strings.
 Its just that us old guys are having a harder time w/ gravity!
 
 
     <mailto:Tump at swnl.net> Tump at swnl.net         <http://www.swnl.net/>
www.SWNL.net
           Solarwinds Northernlights   
   Serving Mid Coast Maine & Northern California
     Me.# 207-832-7574  Cl.#  610-517-8401
 
                          Blair "TUMP" May
      ********  MAINE'S CHARTER ********
            NABCEP    "Certified PV Installer" 
   
      ********  MAINE'S CHARTER ********
   Trace Xantrex "Certified" Dealer / Installer"
   
  

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dana
Sent: Tuesday, December 01, 2009 12:58 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Strings and series of batteries



On a similar subject here -

 

Long ago, I had a Trojan battery rep. state that they did not like to see
more than [12] L-16s in a series -parallel bank system. This was due to too
many points of connection  /  resistance and bad communication due to
multiple flow paths.

 

Has anyone else heard similar or contrary information/recommendations?

 

Thanks

 

 

Dana Orzel

 

Great Solar Works, Inc

www.solarwork.com

E - dana at solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

 

I will be the shift in how the world uses power! - Dana Orzel

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Larry
Crutcher, Starlight Solar
Sent: Tuesday, December 01, 2009 10:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] concord batteries, EQUALIZE Them!

 

If the 180 watt panel will provide enough current to run the recovery
process, then give it a try. What I expect is that your current will vary
throughout the day. Not sure if this is a critical point or if it will just
prolong the process. Pay attention to the temperature. I use a laser temp
probe on the terminals every 30 minutes to verify.

 

Another thing to monitor is the current. It will probably start very low and
build over time due to high resistance from sulfated plates. During this
time the voltage might get really high and then lower some. Don't worry
about the voltage. After a while the current will begin to drop. This means
the recovery process is working. 

 

I just realized that this battery bank must be 4 in series and ten parallel
strings. This is a horrible design that can never work right without
extensive monthly maintenance. The strings with higher resistance will not
be charged properly. Because of this, many strings will be undercharged
every day. EVERY day! So even if you recover these batteries, someone will
need to test and equalize at least every month. I really want to stress this
point as multiple parallel batteries are the ruin and waste of many
thousands of tons of batteries each year. I never design for more than two
strings in parallel. Do this and be happy.

 