[RE-wrenches] Splice Caps
August Goers
august at luminalt.com
Tue Nov 17 19:10:47 EST 2009
Chris -
We use these Panduit C-taps:
http://pdf.directindustry.com/pdf/panduit/panduit-catalog/12722-23882-_455.html
They work great and the compression tool is relatively inexpensive but there is question about whether they're listed for use with solid wire.
-August
August Goers
Luminalt Energy Corporation
O: 415.564.7652
M: 415.559.1525
F: 650.244.9167
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Chris Anderson
Sent: Tuesday, November 17, 2009 1:11 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Splice Caps
What economical splice hardware are people using when you don't have two end of a ground wires to land in the Buchanan Splice Caps? Split bolts are mighty expensive....
-Chris Anderson
Chief Technology Officer
Resources Group
C: 603-732-2411
Borrego Solar Systems
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Peter Parrish
Sent: Tuesday, November 17, 2009 4:04 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Splice Caps
We have been using Buchanan brand "splice caps" to splice two to three #10
Cu EGCs inside 3R-rated j-boxes. Is there an approved methodology for
splicing ECGs under PV modules (i.e. exposed to the elements). I understand
that otherwise listed lay-in lugs are not acceptable for double lugging. -
Peter
Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Click
Sent: Tuesday, November 17, 2009 12:14 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Bonding Rails
Peter,
(1) it appears that per the WEEB installation manual:
http://www.we-llc.com/Datasheets/104-0404-000008-008.pdf
(page 8) you need to have one WEEB per module rather than one for every
other module as you suggest.
(2) 690.43 Equipment Grounding.
Exposed non-current-carrying metal parts of module frames, equipment,
and conductor enclosures shall be grounded in accordance with 250.134 or
250.136(A) regardless of voltage.
I guess the latter answer depends on whether your AHJ considers the
rails "exposed"-- I would, so in this situation I'd have lugs on each
module and each rail.
DKC
-------- Original Message --------
Subject: [RE-wrenches] Bonding Rails
From: Peter Parrish <peter.parrish at calsolareng.com>
To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
Date: 2009/11/17 14:56
> We have been using WEEB clips on all of our installations for over a
> year now. We include the WEEB data/installation sheets in our permit
> package and patiently point out the clips to inspectors who haven't seen
> the WEEB system yet.
>
>
>
> Two questions:
>
>
>
> (1) For ProSolar rails, can we use one WEEB clip to bond two
> adjacent modules (say, modules A and B) on the upper rail (say, rail #1)
> and then use a second WEEB clip to bond the next two adjacent modules
> (say, modules C and D) on the lower rail (say, rail #2) and then use a
> listed lay-in lug (with in our case a WEEB clip) to bond to either rail
> #1 or #2 to continue the grounding?
>
> (2) If we DON"T use WEEB clips and use the conventional bonding
> methodology per module manufacturer's instructions (proper location on
> the module, and listed screws, washers and nuts), do we have to ALSO
> bond the rails? We have an inspector in Pasadena, CA that is requiring
> this, but this is the first time we have been required to do so. Perhaps
> in the past year in ignorant bliss we have missed an important
> development? Or have we been dodging bullets for seven years and not
> even knowing it?
>
>
>
> - Peter
>
> Peter T. Parrish, Ph.D., President
> California Solar Engineering, Inc.
> 820 Cynthia Ave., Los Angeles, CA 90065
> CA Lic. 854779, NABCEP Cert. 031806-26
> peter.parrish at calsolareng.com <mailto:peter.parrish at calsolareng.com>
> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
>
>
>
>
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list