[RE-wrenches] Bonding Rails
Dave Click
daveclick at fsec.ucf.edu
Tue Nov 17 16:09:28 EST 2009
Yes, that's correct. In my answer I was just rephrasing it to say you'd
need twice as many WEEBs as you think. As I understand it, the intent of
this layout is to give the installer two chances to bond each module
properly to the rail.
Unirac has a similar requirement for its UGC-1s on SolarMount, but in
their schematic they don't require you to bond to both rails. So if you
have four modules, you need UGC-1s between A&B, B&C, C&D but you can
have them all on a single rail. I think it's better to alternate between
rails anyway: A&B (top rail), B&C (bottom rail), etc.
DKC
-------- Original Message --------
Subject: Re: [RE-wrenches] Bonding Rails
From: Peter Parrish <peter.parrish at calsolareng.com>
To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
Date: 2009/11/17 15:55
> On page 8 it would appear that we need TWO WEEB clips bonding modules A and
> B to rails #1 and #2 and another TWO WEEB clips bonding modules C and D to
> rails #1 and #2, etc. - Peter
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Click
> Sent: Tuesday, November 17, 2009 12:14 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Bonding Rails
>
> Peter,
>
> (1) it appears that per the WEEB installation manual:
> http://www.we-llc.com/Datasheets/104-0404-000008-008.pdf
> (page 8) you need to have one WEEB per module rather than one for every
> other module as you suggest.
>
> (2) 690.43 Equipment Grounding.
> Exposed non-current-carrying metal parts of module frames, equipment,
> and conductor enclosures shall be grounded in accordance with 250.134 or
> 250.136(A) regardless of voltage.
>
> I guess the latter answer depends on whether your AHJ considers the
> rails "exposed"-- I would, so in this situation I'd have lugs on each
> module and each rail.
>
> DKC
>
> -------- Original Message --------
> Subject: [RE-wrenches] Bonding Rails
> From: Peter Parrish <peter.parrish at calsolareng.com>
> To: 'RE-wrenches' <re-wrenches at lists.re-wrenches.org>
> Date: 2009/11/17 14:56
>
>> We have been using WEEB clips on all of our installations for over a
>> year now. We include the WEEB data/installation sheets in our permit
>> package and patiently point out the clips to inspectors who haven't seen
>> the WEEB system yet.
>>
>>
>>
>> Two questions:
>>
>>
>>
>> (1) For ProSolar rails, can we use one WEEB clip to bond two
>> adjacent modules (say, modules A and B) on the upper rail (say, rail #1)
>> and then use a second WEEB clip to bond the next two adjacent modules
>> (say, modules C and D) on the lower rail (say, rail #2) and then use a
>> listed lay-in lug (with in our case a WEEB clip) to bond to either rail
>> #1 or #2 to continue the grounding?
>>
>> (2) If we DON"T use WEEB clips and use the conventional bonding
>> methodology per module manufacturer's instructions (proper location on
>> the module, and listed screws, washers and nuts), do we have to ALSO
>> bond the rails? We have an inspector in Pasadena, CA that is requiring
>> this, but this is the first time we have been required to do so. Perhaps
>> in the past year in ignorant bliss we have missed an important
>> development? Or have we been dodging bullets for seven years and not
>> even knowing it?
>>
>>
>>
>> - Peter
>>
>> Peter T. Parrish, Ph.D., President
>> California Solar Engineering, Inc.
>> 820 Cynthia Ave., Los Angeles, CA 90065
>> CA Lic. 854779, NABCEP Cert. 031806-26
>> peter.parrish at calsolareng.com <mailto:peter.parrish at calsolareng.com>
>> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
>>
>
>>
>>
>>
>>
>>
>> ------------------------------------------------------------------------
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list