[RE-wrenches] AC coupling induction generators (was Solar and pumped hydro)
Phil Schneider
phil at creativeenergies.biz
Tue Aug 25 19:16:52 EDT 2009
Jay mentions a topic that I've had a question about. Has anybody AC-coupled
an induction generator (wind or hydro) with a conventional battery based
inverter? On the surface it seems that it would work fine as long as there
were appropriate means included in the design to avoid over-charging the
battery. Maybe one of you off-grid hydro Wrenches has done this. Thanks
for any insights...
Phil
On Tue, Aug 25, 2009 at 5:00 PM, jay peltz <jay at asis.com> wrote:
> Hi Keith,
> Sorry about #4, should have said " pumped storage just isn't practical for
> small systems.
>
> So the long version is that to get away from batteries, you would need
> whats called an AC direct hydro.
> This hydro would power the AC loads directly, no inverters, no batteries.
> What gets tricky is that since the hydro has to power EVERYTHING including
> surge it needs to be pretty large for many of todays loads.
> So 8 kw would be pretty small ( about a 4kw inverter system ) and 15kw+ not
> uncommon for an AC direct system.
> Which means you need a lot of water/drop to get this kind of watts from
> your hydro.
>
> In getting away from batteries, inverters etc its a very cost effective and
> reliable system, and really about the ultimate system. Typically these
> systems run for years, decades without problems, with a bit of maintenance
> of course.
>
> Besides the turbine you need a controller system that will keep the voltage
> constant. These use SS controls with diversion loads to keep the voltage
> constant under all loads ( within the parameters of the system) so you don't
> blow things up when the compressor turns off or on for that matter.
> One benefit of these dump loads is that you can make hot water for domestic
> and space heating, air conditioning, leave lights on, you name it.
>
> Hope this makes sense,
>
> jay
>
> peltz power
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090825/2fe0c253/attachment.htm>
More information about the RE-Wrenches
mailing list