[RE-wrenches] NEC Art 310 Ampacity
Peter Parrish
peter.parrish at calsolareng.com
Wed Aug 5 16:45:35 EDT 2009
When we do ampacity calculations, we always use Table 310.16 in Section
310.15 for wire in raceway (EMT, PVC, FMC, LNFC, LMFC), and MC cable. Of
course we use Table 310.15(B)(2)(a) in a raceway or cable with more than
three conductors.
A colleague asked me about the applicability of table B.310.1. It would seem
to apply to 2-3 conductors within an overall covering (multi-conductor
cable) in raceway in free air. Would MC apply? But what in the world is a
"cable, in raceway, in free air"? I'm usually pretty good in parsing this
stuff, but this stumps me.
- Peter
Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885