[RE-wrenches] solid vs stranded AC vs DC
Dave Click
daveclick at fsec.ucf.edu
Wed Aug 5 08:58:53 EDT 2009
2% loss is significant, but I think that Darryl was saying that the
resistance for stranded wire was 2% higher than solid. So if you had a
3% voltage drop in your system with stranded wire, you could rewire the
system with solid wire and have a voltage drop of (3% x 0.98) 2.94% at
peak production; that's less than 1 kWh/yr per kW installed.
DKC
-------- Original Message --------
Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
From: Joel Davidson <joel.davidson at sbcglobal.net>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Date: 2009/8/3 20:31
> 2% loss from any resistance source over 25 years is significant.
>
> ----- Original Message ----- From: "Darryl Thayer" <daryl_solar at yahoo.com>
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Sent: Monday, August 03, 2009 2:04 PM
> Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
>
>
>
> Yes, that is what the code book and my electricians handbook says, but
> 2% is very little. I would think that passing through a conduit hole is
> larger than that.
> Darryl
>
> --- On Mon, 8/3/09, Matt Tritt <solarone at charter.net> wrote:
>
>> From: Matt Tritt <solarone at charter.net>
>> Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
>> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>> Date: Monday, August 3, 2009, 3:49 PM
>>
>>
>>
>>
>>
>>
>> Darryl,
>>
>>
>>
>> Say what?! This would seem to indicate that solid core is
>> actually
>> better for DC than stranded wire. Can this possibly be
>> true??
>>
>>
>>
>> Matt
>>
>>
>>
>> Darryl Thayer wrote:
>>
>> I looked in the code book and found stranded wire
>> has about 2% higher DC resistance than solid, Chapter 9
>> table 8, and that for AC resistance the same value as DC
>> resistance to within the table accuracy Chapter 9 Table 9
>>
>> This table points out that for AC resistance it is
>> important to know the conduit system, as the reactance will
>> have an effect. With AC it is important to never allow a
>> single wire to pass through a metal surface as this will
>> induce eddy currents and magnetic effects into the metal
>> causing voltage drop and heating.
>>
>> --- On Fri, 7/31/09, jay peltz <jay at asis.com>
>> wrote:
>>
>>
>>
>> From: jay peltz <jay at asis.com>
>> Subject: Re: [RE-wrenches] solid vs stranded AC vs DC
>> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>> Date: Friday, July 31, 2009, 10:01 PM
>> Hi Darryl,
>>
>> But what are the differences and when do they come into
>> play?
>>
>>
>>
>>
>> On Jul 31, 2009, at 7:25 PM, Darryl Thayer wrote:
>>
>>
>>
>> Well there is very slight differences between AC
>> and
>>
>>
>> Dc But this
>>
>>
>> difference
>> is so slight that it has no effect on anything we will
>>
>>
>> do.
>>
>>
>> Darryl
>> --- On Fri, 7/31/09, jay peltz <jay at asis.com>
>>
>>
>> wrote:
>>
>>
>>
>> From: jay peltz <jay at asis.com>
>> Subject: [RE-wrenches] solid vs stranded AC
>>
>>
>>
>> vs DC
>>
>>
>>
>> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>> Date: Friday, July 31, 2009, 7:00 PM
>> HI All,
>>
>> I'm trying to understand this wire issue.
>>
>> Whether or not there is a difference between
>>
>>
>>
>> stranded or
>>
>>
>>
>> solid wire for DC or AC.
>>
>> Any takers on this one?
>>
>> thanks,
>>
>> jay
>>
>> peltz power
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>>
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com
>> Version: 8.5.392 / Virus Database: 270.13.42/2279 - Release
>> Date: 08/03/09 05:57:00
>>
>>
>>
>>
>>
>>
>> -----Inline Attachment Follows-----
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list