[RE-wrenches] Power Factor

boB Gudgel boB at midnitesolar.com
Sat Aug 1 14:24:17 EDT 2009


Chris Worcester wrote:
> Has he checked the torque on all the battery connections?
>
> Sincerely,
>
> Chris Worcester
> Solar Wind Works
> NABCEP Certified PV Installer
> Phone: 530-582-4503
> Fax: 530-582-4603
> www.solarwindworks.com
> chris at solarwindworks.com
> "Proven Energy Solutions"
>
>   

Also, Evidence of a bad battery connection (or bad inverter) should be 
obvious if the house lights dim
when the pump tries to start.

boB







> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Matt
> Sent: Thursday, July 30, 2009 3:25 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Power Factor
>
> Possibly a PF question, or maybe one for Magnum - boB,
>
> One of the guys at work is (almost) running a 3/4 hp sub pump with a Magna
> AE 48. Or rather, he isn't. According to him when he first fired it up, it
> operated the pump just fine. The next time he tried, though. he couldn't
> even get a buzz out of the starter. No workee.
>
> The inverter runs all the other loads in the house fine, just not the pump.
> He can run the pump directly from a 7 kW generator with no issues.
> So, do you think we're looking at a power factor deficit,(I think not), a
> motor starter problem or an inverter issue? I have to admit to being
> somewhat baffled by this one because it ran the pump once, but not after.
>
> Matt T
>
>
> ---- boB Gudgel <boB at midnitesolar.com> wrote: 
>   
>> boB Gudgel wrote:
>>
>>  >>So, because of the different ways of specifying PF, it is always best 
>> to think of Power Factor as being the ratio of real (in phase) power, or 
>> VA to reactive power >>(VARS or "Volt Ampere Reactive").   That will 
>> work in all cases.
>>
>>
>> OOOps !   See, this can get confusing.   Reverse what I just said  Power 
>> Factor... " Definition: The ratio of true power to apparent power"  as 
>> David Brearley had just posted.  Otherwise, that calculation can give 
>> you an answer that is GREATER than 1.0 and you don't want that !
>>
>> Had to eat some of my words.  I just wanted to point out that the phase 
>> shift method was called DPF.   Didn't Ian Woodenden do an article on PF
>> recently too ?  If not, he or someone probably should in one of the two 
>> HP magazines.
>>
>> boB
>>
>>     
>>> R. Walters wrote:
>>>       
>>>> Power factor expresses the time difference  between voltage peak and 
>>>> current peak on each of their sine waves. If both current and voltage 
>>>> waves are "in time", (their wave peaks match up) power factor is 1. 
>>>> If one is ahead or behind the other, it's not. Think about an 
>>>> electric motor: we hit it with a voltage wave, and a fraction of a 
>>>> second later, it actually moves, and the current wave happens. There 
>>>> is a little lag there. Resistive loads like lights have very little 
>>>> lag, and big electric motors coming up to speed can have horrible PF.
>>>>         
>>> This definition of power factor only applies for linear loads with 
>>> only inductance or capacitance (with resistance) and is called 
>>> "Displacement Power Factor (DPF) and you will  see that on some power 
>>> meters.
>>>
>>> For non-linear loads, like battery chargers or computer power supplies 
>>> without PF Correction,  the current waveform (on an O-scope) looks 
>>> nothing like a sine or cosine wave.   The current "spikes up" at the 
>>> AC voltage peaks.  It actually *looks like* it might be in phase, BUT 
>>> the current and the voltage do NOT look the same.  It's non-linear.  
>>> Lower than 1.0 power factor for sure.
>>>
>>> For a grid tie inverter, resistive heater or any load that has a PF of 
>>> 1.0,  the current and voltage waveform will both look exactly the same 
>>> AND there will be no phase shift.   They are both linear and all 
>>> current and voltage is in phase at every point in the AC cycle.
>>>
>>> So, because of the different ways of specifying PF, it is always best 
>>> to think of Power Factor as being the ratio of real (in phase) power, 
>>> or VA to reactive power (VARS or "Volt Ampere Reactive").   That will 
>>> work in all cases. (Real Vs. Apparent power is the same thing).   
>>> Apparent power is what you get when you multiply
>>> your RMS meter's Voltage by the RMS current and is called VA Volt 
>>> Amperes)   V x A will be the highest measured number, that is unless 
>>> the PF = 1.0 in which
>>> case both will measure the same.
>>>
>>> Some of that measured VA, or apparent power will be "in phase" and is 
>>> the "real" or "true" power.  Some of that VA may be reactive, 
>>> (inductive or capacitive that is) and is the "out of phase" portion.  
>>> Capacitive and inductive reactance is ALWAYS 90 degrees out of phase 
>>> in current and voltage.... It's just a matter of how MUCH of your 
>>> power is 0 degrees phase shift and how MUCH of that VA is  + or - 90 
>>> degrees out of phase.  If  ALL of the current is in phase with the 
>>> voltage, then
>>> the power factor is 1.0.   That is, if you lay them on top of each 
>>> other, they will look the same on an oscilloscope if power factor = 1.0
>>>
>>> It can get way more complicated that this too, but that's basically 
>>> it.  Feel free to add to this.
>>>
>>> boB
>>>
>>>
>>>
>>> power meters.
>>>
>>>
>>>       
>>>> There is much more to it, with reactance, "real" and "imaginary" 
>>>> numbers?!, etc. but basically, we wrenches need to know that 
>>>> everybody wants  Power factor to be close to 1.
>>>> Obviously there isn't PF on DC, and it is my understanding that most 
>>>> inverters can operate at most power factors. Not 100% sure, but I 
>>>> think GT inverters would help not hurt the PF problem in most 
>>>> situations.
>>>>
>>>> Correct me on any and all of this, Oh fellow wrenches,
>>>>
>>>> R. Walters
>>>> Solarray.com
>>>> NABCEP # 04170442
>>>>
>>>>         
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>
>>>       
>>>> On Jul 30, 2009, at 9:19 AM, boB Gudgel wrote:
>>>>
>>>>         
>>>>> Ron Young wrote:
>>>>>           
>>>>>> Ok, so all seem to be in agreement more or less. How do I break it 
>>>>>> to British Columbia Hydro? :-|
>>>>>>
>>>>>> I think they must be misunderstanding what they are asking for but 
>>>>>> the question is in the section for PV and on the same line as the 
>>>>>> total output in Kwh of the PV. Power Factor %
>>>>>>             
>>>>> It was most likely just  a trick question.
>>>>>
>>>>> You're gonna fool them, though !   :)
>>>>>
>>>>>
>>>>> boB
>>>>>
>>>>>
>>>>>
>>>>>           
>>>>>> I'll contact them and see where this goes but I don't fully 
>>>>>> understand what power factor is which will make it hard to argue my 
>>>>>> case. My understanding is that it is the difference between what 
>>>>>> the utility supplies to a residence vs. the actual loads being used 
>>>>>> by that residence expressed as a percentage. I came across the 
>>>>>> following course offering by SEI that discusses Power Factor with 
>>>>>> reference to PV:
>>>>>>
>>>>>> POWER FACTOR AS IT RELATES TO SOLAR INSTALLATIONS Presented By: 
>>>>>> Michael Smith of Alpine Management Systems  
>>>>>> This session will deal with power factor: What is power factor?  
>>>>>> What causes low power factor?  Why improve your power factor? This 
>>>>>> session will explain the role of power factor correction as it 
>>>>>> applies to solar installations. There are currently over 67,000 
>>>>>> KVAR installations in 26 countries resulting in phenomenal energy 
>>>>>> savings with a corresponding reduction in greenhouse gas emissions. 
>>>>>> Session includes several KVAR installations and the resultant 
>>>>>> savings. 
>>>>>>
>>>>>>             
> http://www.solarenergy.org/workshops/docs/industry08_trainingdetails.pdf 
>   
>>>>>> Ron
>>>>>>
>>>>>> On 30-Jul-09, at 7:43 AM, Wind-sun.com wrote:
>>>>>>
>>>>>>             
>>>>>>> There is no such thing as a power factor for DC or for panels.
>>>>>>>
>>>>>>>               
> ............................................................................
> ...................... 
>   
>>>>>>> Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
>>>>>>> Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
>>>>>>>
>>>>>>>               
> ............................................................................
> ...................... 
>   
>>>>>>>     ----- Original Message -----
>>>>>>>     *From:* Ron Young <mailto:solareagle at solareagle.com>
>>>>>>>     *To:* RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>
>>>>>>>     *Sent:* Wednesday, July 29, 2009 5:45 PM
>>>>>>>     *Subject:* [RE-wrenches] Power Factor
>>>>>>>
>>>>>>>     Can anyone point me in the direction to find the power factor
>>>>>>>               
> for
>   
>>>>>>>     Sanyo HIT N 205 panels? The utility is requesting it on a net
>>>>>>>     metering interconnection application.      Ron Young
>>>>>>>     earthRight Products - Solareagle.com
>>>>>>>
>>>>>>>
>>>>>>>     
>>>>>>>
>>>>>>>               
> ------------------------------------------------------------------------ 
>   
>>>>>>>     _______________________________________________
>>>>>>>     List sponsored by Home Power magazine
>>>>>>>
>>>>>>>     List Address: RE-wrenches at lists.re-wrenches.org 
>>>>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>>     <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>>
>>>>>>>     Options & settings:
>>>>>>>     
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>>
>>>>>>>     List-Archive: 
>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>>
>>>>>>>     List rules & etiquette:
>>>>>>>     www.re-wrenches.org/etiquette.htm
>>>>>>>     <http://www.re-wrenches.org/etiquette.htm>
>>>>>>>
>>>>>>>     Check out participant bios:
>>>>>>>     www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>>>>>
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Home Power magazine
>>>>>>>
>>>>>>> List Address: RE-wrenches at lists.re-wrenches.org 
>>>>>>> <mailto:RE-wrenches at lists.re-wrenches.org> 
>>>>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>>
>>>>>>> Options & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>>
>>>>>>> List-Archive: 
>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>>
>>>>>>> List rules & etiquette:
>>>>>>> www.re-wrenches.org/etiquette.htm 
>>>>>>> <http://www.re-wrenches.org/etiquette.htm>
>>>>>>>
>>>>>>> Check out participant bios:
>>>>>>> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>>>>>>>
>>>>>>>               
>>>>>>             
> ------------------------------------------------------------------------ 
>   
>>>>>> _______________________________________________
>>>>>> List sponsored by Home Power magazine
>>>>>>
>>>>>> List Address: RE-wrenches at lists.re-wrenches.org 
>>>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>
>>>>>> Options & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> List-Archive: 
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> www.re-wrenches.org/etiquette.htm
>>>>>>
>>>>>> Check out participant bios:
>>>>>> www.members.re-wrenches.org
>>>>>>
>>>>>>   
>>>>>>             
>>>>> _______________________________________________
>>>>> List sponsored by Home Power magazine
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org 
>>>>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>
>>>>> Options & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> List-Archive: 
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out participant bios:
>>>>> www.members.re-wrenches.org
>>>>>
>>>>>           
>>>>         
> ------------------------------------------------------------------------
>   
>>>> _______________________________________________
>>>> List sponsored by Home Power magazine
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Options & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> List-Archive: 
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out participant bios:
>>>> www.members.re-wrenches.org
>>>>
>>>>   
>>>>         
>>> _______________________________________________
>>> List sponsored by Home Power magazine
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Options & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> List-Archive: 
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>>
>>> Check out participant bios:
>>> www.members.re-wrenches.org
>>>
>>>
>>>       
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>>     
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>   
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>     
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>   



More information about the RE-Wrenches mailing list