[RE-wrenches] FW: Backup Generators
Allan Sindelar
allan at positiveenergysolar.com
Wed Jul 15 02:24:01 EDT 2009
Wrenches,
This man wrote me about a generator/inverter compatibility problem he's
having. I haven't heard of it before. I suspect it's more than just a simple
voltage-frequency issue, but I haven't heard of this or experienced it. Any
ideas?
Thank you, Allan Sindelar
In the Spring of 08, I purchased a Honda EU6500is generator as a back-up to
my off grid solar system. The Honda was to replace my Yamaha YG6600DE
generator which worked fine with my Trace SW4024 inverter. However the new
Honda inverter-generator seemed to have problems working with my Trace
inverter. If I had a load running, such as my 110 V well pump, it would
handle that load and the excess power from the generator was used to charge
the batteries through the Trace 4024. But once the well pump shut off, the
Honda generator and the Trace didn't seem to like to work together. The
Trace inverter stopped allowing the incoming power to be used to continue to
charge the batteries by disconnecting AC2 power (generator) from coming into
the SW4024. After replacing the Honda with the old Yamaha generator,
everything worked fine again, including charging the batteries without
another load on the inverter.
As a result of the above, my question is: Have you experienced similar
incompatibility with inverter-generators and inverters such as my Trace
SW4024? If so, do you have any suggestions that will allow me to use my
Honda EU6500is with my Trace 4024? Calls to Xantrex and Honda on this issue
did not provide any useful information.
Thank you, Michael
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090715/54e7f4e7/attachment.htm>
More information about the RE-Wrenches
mailing list