[RE-wrenches] fronius IG Plus practical engineering WAA???

Darryl Thayer daryl_solar at yahoo.com
Sun Jun 28 00:01:21 EDT 2009


If I use the Hu361 (unfused) it has the 30 amp rating, the 80% reduction only applies if I use fuses per the continuous operation derating for overcurrent devices.  The switch is not a conductor or overcurrent device.  If I use the H361 (fused) then the 80% derate applies, (24 amps) and if I use the double break I am limited to 18 amps in all cases.

Darryl
Correct?  

--- On Sat, 6/27/09, Phil Undercuffler <solarphil at gmail.com> wrote:

> From: Phil Undercuffler <solarphil at gmail.com>
> Subject: Re: [RE-wrenches] fronius IG Plus practical engineering WAA???
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Saturday, June 27, 2009, 10:47 PM
> They added a special listing, where
> they were able to expand the range of their heavy duty
> switch when used in PV direct applications. The special PV
> listing doesn't void the standard wiring methods,
> however.  You can still run the full 30 amps (24 * 1.25)
> through two poles series connected, or you can bring
> multiple subarrays through each of the poles, each with a
> lower individual Isc limit but with an aggregate higher
> current capacity.  
> 
> This really becomes handy on the larger 60 and
> 100A disconnects.  Suddenly, a 3 pole 100A disconnect can
> be used for three large subarrays to a central inverter,
> which saves considerably on BOS costs.  Also, be aware that
> (the last I looked) the special listing doesn't apply to
> their 200A and larger disconnects.
> 
> 
> 
> Phil Undercuffler
> 
> --------
> 
> 
> 
> 
> 
> On Sat, Jun 27, 2009 at 9:22 PM,
> Darryl Thayer <daryl_solar at yahoo.com>
> wrote:
> 
> 
> 
> Again this is FMI for my information, Did not Square D
> change there rating for PV systems?
> 
> Darryl
> 
> 
> 
> --- On Fri, 6/26/09, Phil Undercuffler <solarphil at gmail.com>
> wrote:
> 
> 
> 
> > From: Phil Undercuffler <solarphil at gmail.com>
> 
> > Subject: Re: [RE-wrenches] fronius IG Plus practical
> engineering WAA???
> 
> <snip>
> 
> >
> 
> > This confirmed my understanding
> 
> > that the limiting factor
> 
> > on the 30A switch
> 
> >
> 
> > in a photovoltaic applications is
> 
> > not 30A * 0.8.  The limiting factor
> 
> > is 18A
> 
> >
> 
> > per pole or 11.5A Isc per pole.
> 
> >
> 
> > <unsnip>
> 
> >
> 
> >  
> 
> >
> 
> > To clarify – the 18A per pole /
> 
> > 11.5A Isc per pole only
> 
> > applies if you are using the limited listing for PV
> 
> > applications, with one
> 
> > string or subarray per pole.  If you
> 
> > wire
> 
> > the HU361RB disconnect with two poles connected in
> series,
> 
> > then you may run the
> 
> > switch at 100% of its rating. 
> 
> >
> 
> >  
> 
> >
> 
> > Therefore, you can stuff up to 24
> 
> > amps Isc (24 * 1.25 =
> 
> > 30) through a single disconnect if the poles are wired
> in
> 
> > series, or you can
> 
> > run 3 subarrays each with no more than 11.5A per pole
> if
> 
> > wired in
> 
> > parallel. 
> 
> >
> 
> >  
> 
> >
> 
> > Sometimes it’s good to have
> 
> > options.
> 
> >
> 
> >  
> 
> >
> 
> >  
> 
> >
> 
> >  
> 
> >
> 
> > Phil Undercuffler
> 
> >
> 
> > Director, Battery-based and
> 
> > Off-grid
> 
> >
> 
> > Distribution Sales Group
> 
> >
> 
> > Conergy
> 
> >
> 
> > Our World Is Full of Energy
> 
> >
> 
> > 1730
> 
> > Camino Carlos Rey Suite 103
> 
> >
> 
> > Santa
> 
> > Fe, NM  87507
> 
> >
> 
> > p.undercuffler at conergy.us
> 
> >
> 
> > Direct
> 
> > |
> 
> > 505.216.3841
> 
> >
> 
> > Toll Free | 888.396.6611 x4841
> 
> >
> 
> > Fax | 505.473.3830
> 
> >
> 
> > www.conergy.us
> 
> >
> 
> >
> 
> >
> 
> > -----Inline Attachment Follows-----
> 
> >
> 
> > _______________________________________________
> 
> > List sponsored by Home Power magazine
> 
> >
> 
> > List Address: RE-wrenches at lists.re-wrenches.org
> 
> >
> 
> > Options & settings:
> 
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> >
> 
> > List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> >
> 
> > List rules & etiquette:
> 
> > www.re-wrenches.org/etiquette.htm
> 
> >
> 
> > Check out participant bios:
> 
> > www.members.re-wrenches.org
> 
> >
> 
> >
> 
> 
> 
> 
> 
> 
> 
> _______________________________________________
> 
> List sponsored by Home Power magazine
> 
> 
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> 
> 
> Options & settings:
> 
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> 
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> 
> 
> List rules & etiquette:
> 
> www.re-wrenches.org/etiquette.htm
> 
> 
> 
> Check out participant bios:
> 
> www.members.re-wrenches.org
> 
> 
> 
> 
> 
> 
> -----Inline Attachment Follows-----
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 


      


More information about the RE-Wrenches mailing list