[RE-wrenches] fronius IG Plus practical engineering WAA???
Darryl Thayer
daryl_solar at yahoo.com
Sat Jun 27 23:22:18 EDT 2009
Again this is FMI for my information, Did not Square D change there rating for PV systems?
Darryl
--- On Fri, 6/26/09, Phil Undercuffler <solarphil at gmail.com> wrote:
> From: Phil Undercuffler <solarphil at gmail.com>
> Subject: Re: [RE-wrenches] fronius IG Plus practical engineering WAA???
<snip>
>
> This confirmed my understanding
> that the limiting factor
> on the 30A switch
>
> in a photovoltaic applications is
> not 30A * 0.8. The limiting factor
> is 18A
>
> per pole or 11.5A Isc per pole.
>
> <unsnip>
>
>
>
> To clarify – the 18A per pole /
> 11.5A Isc per pole only
> applies if you are using the limited listing for PV
> applications, with one
> string or subarray per pole. If you
> wire
> the HU361RB disconnect with two poles connected in series,
> then you may run the
> switch at 100% of its rating.
>
>
>
> Therefore, you can stuff up to 24
> amps Isc (24 * 1.25 =
> 30) through a single disconnect if the poles are wired in
> series, or you can
> run 3 subarrays each with no more than 11.5A per pole if
> wired in
> parallel.
>
>
>
> Sometimes it’s good to have
> options.
>
>
>
>
>
>
>
> Phil Undercuffler
>
> Director, Battery-based and
> Off-grid
>
> Distribution Sales Group
>
> Conergy
>
> Our World Is Full of Energy
>
> 1730
> Camino Carlos Rey Suite 103
>
> Santa
> Fe, NM 87507
>
> p.undercuffler at conergy.us
>
> Direct
> |
> 505.216.3841
>
> Toll Free | 888.396.6611 x4841
>
> Fax | 505.473.3830
>
> www.conergy.us
>
>
>
> -----Inline Attachment Follows-----
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
More information about the RE-Wrenches
mailing list