Hi Jeff,

I am not sure if this relates to your issue but there is an issue with  
Magnum inverters and Splindide washers. Splindide will not work on a  
Magnum sine wave. They are aware of this. Here is a copy of my old  
post to the list:

....I have a recent power issue come up with a Magnum inverter. A  
customer tried to operate her Splindide washer/dryer but the motor  
would not start. I looked at the waveform with a scope and RMS voltage  
and frequency were fine. The waveform looked good until the motor  
tried to start. The washer was putting a jagged noise riding on the  
sine wave. The voltage and waveform still looked OK other than the  
noise. I was mostly sure that this was the cause so I grabbed a 600  
watt cheap import sine wave inverter and connected the washer. Same  
ripple was present on the waveform but the $400 inverter would run the  
washer motor fine. It also runs fine with a 1600 watt Honda inverter/ 
generator.


Larry Crutcher
Starlight Solar
(928) 941-1660
Renewable Energy Products, Service and Installation

On Jun 18, 2009, at 4:44 PM, Jeff Oldham wrote:

> Not sure if anyone offered this already - The DR will do a 5 sec.  
> surge to 6200W the Outback will do a 5 sec. surge to 4800W. This is  
> common, most mod's will surge considerable more than Sine's, that is  
> the big trade off other than power quality and tare losses. In  
> addition I'm very skeptical that the Staber only surges to 11A, have  
> you measured the actual surge? When I replaced my good 'ol Trace  
> 2512 (too many appliances disliked the mod. sine) and went to a  
> Magnum 2812 my washer would kick it out as my washer surged to 31A  
> and the Mag. would do 30! This is a modern Horz. axis machine. I now  
> have the Magnum and a new Vanner ITC 12-3200W that does a 3 sec.  
> surge to 6400W and will even run my wire welder and air compressor,  
> both used to be genny only loads.
>
> -jeff o
>
>
> From the Solar, Wind and Hydro powered office of Jeff Oldham/ 
> Regenerative SOLutions
>
>
>
> ____________________________________________________________
> Save on Moving Supplies. Click Here!
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090618/ab8ffb2d/attachment.htm>


More information about the RE-Wrenches mailing list