William,

In the Xantrex "XW Power System Installation Guide", pages 2-34 to 2-37, there is a parts list and some diagrams on the wiring of a 3-inverter system. The parts list calls for two 5 ft (62" hole-to-hole) 4/0 battery cables to connect the third inverter up to the Distribution Panel.

Also shown is the use of an external bypass switch to make up for the lack of enough AC breaker spaces in a single Distribution Panel. It shows a breaker/interlock panel, but a 2-pole manual transfer switch will also work. Either way, it should be rated for at least 200A.

Brian Teitelbaum
AEE Solar



From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
Sent: Tuesday, April 28, 2009 8:49 PM
To: RE-wrenches
Subject: [RE-wrenches] 3 Xantrex XW system

Friends:

We are in the midst of installing our first 3 XW system.  Several questions arose during our work today.  I appreciate input any of you might have.

1.  Did you find the leads from the Xantrex connection ki long enough for the third inverter?

2.  How many AC sources did you connect?

3.  Did you provide bypass capabilities?

4.   How did you interlock the bypass capabilities?

5.  Did you use one or two Power Distribution Panels?

6.  Can you offer any advice on how best to connect this equipment?

Thanks in advance.

William Miller



Please note new e-mail address and domain:

William Miller
Miller Solar
Voice :805-438-5600     Fax: 805-438-4607
email: william at millersolar.com
http://millersolar.com
<http://millersolar.com/>License No. C-10-773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090428/c64d2893/attachment.htm>


More information about the RE-Wrenches mailing list