[RE-wrenches] Outback GTFX errors

William Miller william at millersolar.com
Fri Apr 10 02:39:47 EDT 2009


Jon:

1. Outback inverters are notorious for reporting errors incorrectly.  Often 
the errors are a clue, but not the actual error. As an example, a shorted 
AC output might report a "Low Battery Voltage" error because when the 
output is shorted, the battery draw is momentarily very high, reducing it's 
voltage.  Look for a related symptom.

Have you been able to monitor the AC voltage during inverter sell 
operation?  High AC voltage in a grid-tie system can be caused by actual, 
intermittent high grid voltage and/or inadequate feeder size, allowing the 
inverter to push up the voltage at the inverter end of the feeder.  I've 
seen a bad breaker cause this as well.  In any of these described cases, 
the inverter error reporting would be accurate.

2. Outback sends out a standard kit of three field-replaceable boards.  You 
rarely need to replace all of the boards.  You need to figure out which 
board(s) to replace or, ask tech support.  I guess when in doubt, one could 
replace all three.  It appears you have narrowed the problem down to not 
one of the three boards.

Good luck.

William Miller




At 08:28 PM 4/9/2009, you wrote:
>I have a customer with an Outback GTFX 3048 that has an"over voltage
>AC in" warning but when I check the voltage with my Fluke meter it
>shows a normal range 122 - 126 V . In the Mate grid menu the AC high
>Volts is set at 140 V . The customer called Outback support before I
>could get to him and they told him he needed to have me change all 3
>boards out. They sent the boards so I went ahead and changed them
>out, but the same error occurred again. We called Outback support
>again but did not get a satisfactory answer on how to fix it.
>
>Has anyone else run into this problem ? I suspect the Mate may be flaky.
>
>Jon
>
>Jon Haeme Innovations
>Kempton, IL _______________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20090409/6b0d3eae/attachment.htm>


More information about the RE-Wrenches mailing list