[RE-wrenches] Mixing and Matching PV modules--Error Corrected

Bill Brooks billbrooks7 at yahoo.com
Tue Mar 31 15:55:15 EDT 2009


Peter,

Put 7 type A personality modules in one string and 6 Type B, plus 1 Type A.
The Type A in the Type B string will just act like one of the Type B boys.
No stress, just chillin' a slight bit off max power current. That will be
better than mixing both strings with high and low current modules. 

In the old days (1980s) we would current match strings as best we could, so
what you describe was a common occurrence. Keep all the modules of one
current in one string. If you must mix, one or two higher current modules
are always okay, but one or two lower current modules will hold up the whole
string.

Summarizing:

7 Type A in string 1
6 Type B and 1 Type A in string 2

Happiness will be found in this arrangement.


Bill.



-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Peter
Parrish
Sent: Tuesday, March 31, 2009 10:13 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Mixing and Matching PV modules--Error Corrected

[Bill: I think our disagreement a while ago had to do with the dependence of
Voc and Vmp with insolation. I said there was one and you said there wasn't.
The way I resolved it in my mind is that there is a small change in Voc with
insolation as well in Vmp, but to zeroth order one could ignore the change
for most practical calculations.]

I should have mentioned this, but I don't have the luxury of putting
together a string of type A and string of type B. I have 8 of type A while I
have only 6 of type B. I wish I did have 8+8 but I only have 8+6 and I
wanted to use them all (I am guilty of optimizing). It seemed a shame to go
the 6+6 route, and I'd guess I'd have to do some research on low voltage,
grid tied inverters (I think even a Fronius needs 8 module strings).

So, if I accept the lower operating current, limited by the type B modules,
in a split string...will this stress out the type B modules in the string?

- Peter

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com 


-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Monday, March 30, 2009 5:57 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Mixing and Matching PV modules--Error Corrected

Peter,

Although last time we discussed, you didn't seem to agree with me, I guess
I'll try responding to this question.

The best situation is to keep the two strings of modules in their own
strings. 7 of the older in series, paralleled with the 7 of the newer in
series. The operating voltages, and open circuit voltages are for all
practical purposes--identical. It appears that the only difference is the
size of the cell--producing a higher current as expected--with little or no
change in voltage. Operating voltage is the key--as in our last discussion.


Mixing the strings will result in lower output overall. Perhaps trying it
both ways would prove it to you. An I-V curve tester will clearly show the
benefit of not mixing the modules within the string. As I teach my classes,
you have to think like a "PV". The I-V curve is limited by the lower current
modules in both strings if you wire as you suggest. If you wire the modules
with the like modules, each string will produce their maximum current.

Draw out the I-V curves and it may make more sense. 

Bill.


-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Peter
Parrish
Sent: Monday, March 30, 2009 3:50 PM
To: 'Peter Parrish'; 'RE-wrenches'
Subject: Re: [RE-wrenches] Mixing and Matching PV modules--Error Corrected

I think I understand all the dictums about single-strings of PV modules: all
the same modules, all the same azimuth and tilt, but I have a "special
situation".

We are starting to accumulate a number of "second hand" PV modules. Some
have frames slightly damaged by the shipper; some have come from warranty
replacements; and some are odd lots that we haven't been able to sell.

What I want to do is to set up a demo system composed of two different types
of modules. This is my initial design:

Total of fourteen modules. Two strings of seven modules each. Each string
consisting of four modules of one type (type A) and three modules of a
second type (type B).

Both module types have 50 cells and the type A module has 155mm-sq cells and
the type B module has 150mm-sq cells. So you would think that the
performance specs would match pretty well. However, since the type B modules
are an earlier vintage, they probably don't have the latest and greatest
surface treatment, etc., so the current specs are lower than one might
expect.

Specs on type A: Voc = 30.8V, Vmp = 24.5V, Isc = 8.70A, Imp = 8.16A. Specs
on type B: Voc = 30.6V, Vmp = 24.6V, Isc = 7.38A, Imp = 6.93A. 

So here's my question: would putting together the strings of four type A and
three type B cause any problems? I know the string current would be limited
by the type B modules, but above and beyond that, what would be the
operating point of the type A modules and what would be the stress if any on
the type B modules? I'd like this demo system to last a while and I
certainly don't want to see scorch marks on the type B modules after a few
months of use. 

Any thoughts?

- Peter

Peter T. Parrish, President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com 



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



More information about the RE-Wrenches mailing list