[RE-wrenches] Back feeding battery inverter with grid-tie inverter
Jon Haeme
jjhaeme at stelle.net
Mon Jan 19 10:13:59 EST 2009
This is not a good combination of equipment choices. If you want a
safe and reliable installation it is good practice to use equipment
as it is intended to be used. You should not back feed an Xantrex XW
through the output side. The easiest way to go is use a Sunny Island
with the batteries in the garage instead of the XW. However if you
already have the XW in place then I would suggest using the Apollo
T80HV charge control as suggested by Daryl . It has a max of 200 VOC
at 80 amps . Why make it more complicated than it needs to be ?
Jon
Jon Haeme Innovations
Kempton, IL
NABCEP certified PV installer #102503-19
On Jan 18, 2009, at 11:31 PM, Jeff Yago wrote:
> I know this subject has come up before, but there have been several
> different suggested ways to handle the problem and I was hoping for
> easiest. We install lots of both on grid and off grid systems.
> However, we have a client that will require a ground mounted array
> much futher away from the inverter and batteries in the garage than
> we normally would want to do since the voltage drop for this long
> distance would be excessive at low voltage even with large cables.
> We have decided to locate a weather-proof sunnyboy grid-tie
> inverter at the array, and supply 120/240 volts to the critical
> loads sub-panel which is supplied by a Xanrex XW inverter and
> battery bank in the garage. I realize there are several design
> issues here when the grid is down, since we want the grid-tie
> inverter to remain on but be blocked from the grid by the Xantrex
> inverter.
>
> The question is, what is the best way to keep a load on the
> sunnyboy since it will not be grid connected during an outage.
> Also, is there a best way to feed the output from the Sunnyboy to
> the Xantrex that does not just power the sub-panel loads during an
> outage, but also will re-charge the battery bank through the Xanrex?
>
> If you back-feed the Xanrex from the sub-panel it is normally
> supplying with output from the Sunnyboy, will the Xanrex see this
> input and think the grid is up and be able to re-charge the battery
> bank?
>
> Will we need any separate transfer switches or power relays?
>
> Thanks,
>
> Jeff Yago
>
> _____________________________________________________________
> Netscape. Just the Net You Need.
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list