The formulas I learned in school are:
Single-Phase Vd = (2 * d * k * I) / cm
where: d = distance; the constant k = 12.9 Ohms for Cu & 21.2 Ohms for AL; I
= current; cm = circular mils
3-Phase Vd = (1.73 * d * k * I) / cm
My note are failing me, but I believe d is actually the one-way distance.
This is multiplied by 2, in the single-phase calculation, to account for the
round trip distance. In the 3-phase calculation 1.73 is used instead. Table
8 in the NEC has the conductor properties. This is where I always look up
circular mils.
In the past I¹ve run these calculations against my ElectriCalc & had things
check out.
>
> I feel kinda foolish in asking this.....but when calculating voltage drop in a
> conductor over distance, do I use the one-way or round-trip distance? thanks,
> marco Marco Mangelsdorf, Ph.D., President
> Electrical Contractor License C-26351
> 69 Railroad Avenue, Suite A-7
> Hilo, Hawaii 96720 USA
> (808) 969-3281, fax 934-7462 www.provisiontechnologies.com
> <http://www.provisiontechnologies.com/>
>
>
>
>
> David Brearley, Technical Editor
> SolarPro magazine
> NABCEP Certified PV Installer
> david.brearley at solarprofessional.com
> Direct: 541.261.6545
> Fax: 541.512.0343
>
> Visit our Web site at solarprofessional.com