Almost right Christopher.  NEC 705.12(2) allows the ratings of the 
overcurrent devices supplying power to the bus bar to be 120% of the 
busbar rating.  For a 225-amp busbar that amounts to 270 amps.  So a 
200-amp main breaker and a 70-amp back fed breaker from the solar 
system.  Or a 225-amp main breaker and a 45-amp back fed breaker from 
the solar system.


Christopher Freitas wrote:
> Ahhh – I think I get it – you get the 20% of the 200 amps (so 40 amps) + 
> the extra 25 amps because the buss is only running at 200 amps?
> 
>  
> 
> I just saw you emailed me… 
> 
>  
> 
> Christopher
> 
>  
> 
>  
> 
> Christopher Freitas
> 
> Director of Research and Development
> 
> OutBack Power Systems, Inc.
> 
> cfreitas at outbackpower.com <mailto:cfreitas at outbackpower.com>
> 
> Tel 360 435 6030
> 
> Cell 360 202 4239
> 
> 19009 62^nd Ave NE
> 
> Arlington WA 98223 USA
> 
> www.outbackpower.com <http://www.outbackpower.com/>
> 
> ------------------------------------------------------------------------
> 
> *From:* re-wrenches-bounces at lists.re-wrenches.org 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *David 
> Brearley
> *Sent:* Thursday, December 04, 2008 11:41 AM
> *To:* RE-wrenches
> *Subject:* Re: [RE-wrenches] Square D 225A load center
> 
>  
> 
> It has an option for a factory-installed 200A main breaker.
> 
> 
> On 12/4/08 12:31 PM, "Christopher Freitas" <cfreitas at outbackpower.com> 
> wrote:
> 
> How does the 225 amp rating make it ideal for 60 amp breakers?  20% of 
> 225 amps is 45 amps – and even with “rounding up� it only gets you to 50 
> amps.  
>  
> 
> Christopher
> 
>  
> Christopher Freitas
> Director of Research and Development
> OutBack Power Systems, Inc.
> cfreitas at outbackpower.com <mailto:cfreitas at outbackpower.com>
> Tel 360 435 6030
> Cell 360 202 4239
> 19009 62nd Ave NE
> Arlington WA 98223 USA
> www.outbackpower.com <http://www.outbackpower.com/>
> 
> ------------------------------------------------------------------------
> 
> *From:* re-wrenches-bounces at lists.re-wrenches.org 
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] 
> <mailto:re-wrenches-bounces at lists.re-wrenches.org%5d> *On Behalf Of 
> *Andrew Truitt
> *Sent:* Thursday, December 04, 2008 8:33 AM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] Square D 225A load center
> 
> 
> 
> 
> Greetings all!  I heard that Square D makes a load center with a 225A 
> buss bar and a 200A main breaker - ideal for installing 60A of solar 
> interconnection breakers.  Does anyone have a part number (or any other 
> info) on this item?
> 
> Thanks!
> 
> 
> Andrew Truitt
> Standard Solar
> 
>  
> 
> MESSAGE CONFIDENTIALITY NOTICE:
> This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited.  Please reply to the sender that you have received the message in error, then delete it. Thank you.



More information about the RE-Wrenches mailing list