Soldering is not restricted by the NEC - see section 110.14 "Electrical
Connections" for details.  

 

Properly crimped connections can be as reliable and are electrically
similar to properly done crimped AND soldered connections (the NEC does
not allow soldered only connections - perhaps that was what you meant?
See 110.14(B) for that restriction.) 

 

I do not think that soldering skills is a "must have" requirement for a
solar installer technician anymore - other than for plumbing - which is
a different thing.     

 

Christopher

 

 

Christopher Freitas

Director of Research and Development 

OutBack Power Systems, Inc.

cfreitas at outbackpower.com <mailto:cfreitas at outbackpower.com> 

Tel 360 435 6030

Cell 360 202 4239

19009 62nd Ave NE 

Arlington WA 98223 USA

www.outbackpower.com <http://www.outbackpower.com/> 

 


MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited.  Please reply to the sender that you have received the message in error, then delete it. Thank you.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20081203/8b464e29/attachment-0001.htm>


More information about the RE-Wrenches mailing list