[RE-wrenches] utility EDS signage
Kent Osterberg
kent at coveoregon.com
Thu Nov 20 02:24:59 EST 2008
Phil,
NEC 690.17 says "Where all terminals of the disconnecting means may be
energized..." It would take a pretty rare malfunction of a grid
connected inverter to energize the load terminals of the utility
disconnect. But we have some AHJs that require this label on every ac
disconnect, all the way back to the utility meter, anyway. The warning
is appropriate on the dc disconnect of almost all inverters because the
capacitors in the inverter take a few minutes to bleed off.
To me, the bigger hassle are plaques required by 705.10. Can anyone
give me a reasonable explanation for their value in a utility
interactive system? I can understand if there is a grid backup system -
emergency personnel may need to know where to turn off the backup power;
but a grid interactive inverter shuts down when there service is shut
down. It seems to me that this plaque is likely to send an emergency
responder on a wild goose chase.
Kent Osterberg
Blue Mountain Solar
Phil Schneider wrote:
> Wrenches,
>
> Our utilities require an external AC disconnect between the inverter and the
> point of interconnection, located next to the meter. In the past, we have
> marked this switch with the language in 690.17 (although no AHJ or utility
> has required it). Because we generally argue against the necessity of this
> switch, I don't feel it is accurate to say that "terminals on both the line
> AND load sides may be energized in the open position".
>
> Do other Wrenches post this plaque? Is there a way that both line AND load
> terminals of this switch could be energized? (other than an inverter not
> paying attention to its UL listing?)
>
> Thanks again for your thoughts,
> P.
>
> Phil Schneider
> Creative Energies
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> ------------------------------------------------------------------------
>
>
> No virus found in this incoming message.
> Checked by AVG - http://www.avg.com
> Version: 8.0.175 / Virus Database: 270.9.7/1798 - Release Date: 11/18/2008 8:59 PM
>
More information about the RE-Wrenches
mailing list