Eric -
The minimum battery size we recommend for AC coupled applications is
about 100 amp-hours at 48VDC - roughly 4kWH at 80% DOD - this allows
good motor starting performance and provides the necessary stability for
the battery-less grid-tie inverter to continue powering loads.
Smaller batteries have been used successfully - but they need to be
either very high performance / low impedance (such as Optima type
batteries) or the loads need to be very modest with little starting
surge requirements. The cost for the smaller Optimas is usually the
same as the larger sealed AGM batteries so they do not make sense to me
to use unless the smaller / lighter benefits are needed (such as in a
portable display for example).
Let me know your specifics and I will work up so recommendations.
Christopher
Christopher Freitas
Director of Research and Development
OutBack Power Systems, Inc.
cfreitas at outbackpower.com <mailto:cfreitas at outbackpower.com>
Tel 360 435 6030
Cell 360 202 4239
19009 62nd Ave NE
Arlington WA 98223 USA
www.outbackpower.com <http://www.outbackpower.com/>
________________________________
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Eric
Andrews
Sent: Tuesday, November 04, 2008 10:56 PM
To: RE-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] AC coupling
Fellow PV Techies -
When designing an AC coupled PV system using Outback: Am I correct that
the battery bank can be minimally small, as they are just there to power
the GVFX Output and mimic the grid for the grid-tied inverter of choice?
Thanks,
Eric R. Andrews
NABCEP Certified PV Installer
Eco Solar, Inc.
Klamath Falls, OR 97601
MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you.