[RE-wrenches] Charging with "no contact" systems
jay peltz
jay at asis.com
Tue Sep 30 11:11:16 EDT 2008
HI Walt,
Have you looked into the IBE industrial battery chargers?
They will be large enough and robust enough to handle the charging.
I'm not sure if they are the best for constant charging however. But
maybe that isn't a large problem given the condition of the electric
grid?
Jay
Peltz power
On Sep 30, 2008, at 7:57 AM, Walt Ratterman wrote:
> Hello all,
>
> We have an application in Haiti (and some African countries as well)
> where we have inverter /battery systems on a lousy (very lousy)
> grids. The grid is good enough to charge batteries, but not
> sufficient for sensitive electronic loads.
>
> Therefore, the systems we are using are three Outback FX 3648
> inverters. If they are connected with AC IN from the grid and the
> grid is on and is lousy (but good enough to get through the voltage
> and frequency limits), then this power will be passed on to the
> computers. (The reality is that we have to open the voltage window
> too wide to let the grid in at all, and thus unacceptable to the
> electronics.) So, we DO NOT connect the AC IN to the inverters. In
> other words, the FX units become inverters only, and never pass AC
> current from the grid to the loads. (This is what we are calling
> “no contact” system – similar to a double conversion UPS
> system.)
>
> So – we need to add separate battery charging to the battery bank
> that will put in roughly equal amphours to what we feel the daily
> usage will be during the day.
>
> The load is about 8000 watts, which might translate to 140 to 170
> amps of discharging. We might not have to put in the full amount of
> charge, since our charging can continue in the night hours when the
> load is not discharging, but we should probably try to charge the
> batteries at around 100 to 140 Amps DC (48V).
>
> Does anyone have a recommendation as to the type of charger that
> might work best for this, either bulk, or smart, or a combination?
> OR……other suggestions for this system that I am just missing??
>
> We would plan to monitor this system by using the FlexNET DC system,
> adding a DC shunt on the negatives of the feed going from the
> charger TO the batteries.
>
> Thanks,
>
> Walt
>
> Walt Ratterman
> SunEnergy Power International
>
> 11 Laurel Lane South Washougal, WA 98671
> (360)-837-3680 ▪ fax (360)-837-1315 ▪ Skype Walt-Mobile
> wratterman at SunEPI.org ▪ www.SunEPI.org
>
>
>
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus
> signature database 3483 (20080930) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20080930/a9580545/attachment-0001.htm>
More information about the RE-Wrenches
mailing list