On Aug 22, 2008, at 7:40 AM, Travis Creswell wrote:
> 1 ton = 12,000 BTU's
>
> SEER = how many BTU's per kW (Since you asked about "rough
> electrical load"
> for this equation we're going to ignore the complexities for EER
> vs. SEER,
> COP at varying outdoor temps and so on. We'll leave that for
> someone else
> to discuss if they desire)
>
> Plus you'll want to add approximately 150 watts per ton for the air
> handler
>
> Assuming a 13 SEER AC unit the math is;
>
> 2.5 tons x 12,000 BTU's = 30,000 BTU's
>
> 30,000 BTU's/13 SEER= 2.3 kW
>
> 2.5 tons x 150 watts/ton for air handling = 375 watts
>
> For a total running kW of ~2.7.
>
> That's how I do it. Doesn't mean it's the right or only way.
>
> Best,
> Travis Creswell
> Ozark Energy Services
>
>
>
> -----Original Message-----
> From: re-wrenches-bounces at lists.re-wrenches.org
> [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay
> peltz
> Sent: Friday, August 22, 2008 9:23 AM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] offgrid system question
>
> Can someone tell me how to convert AC "tons" to rough electrical load?
> or is there a way?
>
> I've got a customer who is wanting to install a AC unit and they tell
> me its a 2.5 ton and uses 9000 watts.
> ( they haven't given me make or model yet)
>
> thanks,
> jay
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> RE-wrenches at lists.re-wrenches.org
>
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
> No virus found in this incoming message.
> Checked by AVG.
> Version: 7.5.526 / Virus Database: 270.6.6/1627 - Release Date:
> 8/22/2008
> 6:48 AM
>
>
> No virus found in this outgoing message.
> Checked by AVG.
> Version: 7.5.526 / Virus Database: 270.6.6/1627 - Release Date:
> 8/22/2008
> 6:48 AM
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> RE-wrenches at lists.re-wrenches.org
>
> http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
More information about the RE-Wrenches
mailing list