Phil,

Have you clamped this circuit to see what the actual amps are?

Matt T

Phil Schneider wrote:

>Wrenches,
>
>We have an off-grid system (quad OB 3648s, two MX60s) with an MX60 output
>breaker that is tripping unexpectedly, and haven't been able to troubleshoot
>the problem.
>
>The MX60 circuit with the problem has 16 Mitsubishi 170s (on a dual axis
>tracker) and a 60A DC breaker between the MX and the DC positive bus.  When
>operating, the MX generally shows less than 50A on the battery side in peak
>charging conditions.
>
>The owner is charging a RAV4 EV on a 240VAC, 50A circuit.  The MX output
>breaker in question trips when this load is turned on.  This happens
>regardless of battery SOC - even when MXs are in float.  Limiting the MX to
>45A output did not work either.  The other MX also has 16 Mitsu 170s, but
>they are fixed and do not have this problem.
>
>The breakers have been switched out (with equivalent 60A breakers) with no
>effect.  All terminations on the DC side have been checked.  MX #6 wiring is
>being upgraded to #4 right now, with 70A breakers.
>
>Outback was stumped.  Any other ideas out there?  Thanks...
>
>P.
>
>Phil Schneider
>Creative Energies
>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>RE-wrenches at lists.re-wrenches.org
>
>http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>http://www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>No virus found in this incoming message.
>Checked by AVG - http://www.avg.com 
>Version: 8.0.138 / Virus Database: 270.5.12/1590 - Release Date: 8/4/2008 8:09 AM
>
>
>
>  
>


More information about the RE-Wrenches mailing list