jryago at netscape.com wrote:
>
> I attended an XW training program last fall in Long Beach and thought
> this new inverter had some great design features over others we have
> been installing. I recently purchased several XW inverters including
> all options for stock but as yet have not found an application.
> However, I have heard a few comments here and from others who have
> installed XW systems and have described a few "bugs" they had to deal
> with. Since most of these related to software problems, I assume they
> are easy to correct, but I do not know if these are being addressed at
> this time, are going to be addressed, or updated software is already
> available for us to download into inverters already purchased.
>
> Having replaced boards in Outback inveters with little trouble, I was
> concerned to hear that Xantrex is not allowing board replacement in the
> field and hope someone on this list can address these concerns,
>
Mick says: Part #865-1155 is a (fairly expensive) adapter to connect the
USB port on a Windows computer into the Xanbus network. The Windows
software is called XW config, and if you have a sufficiently recent
version you can update the firmware on XW products. I did this just last
night. My first update attempt failed, but not before erasing the
inverter and the charge controller. Awkward.
I did finally manage to complete the upgrade but I had to read between
the lines on the instruction .pdf. The most recent firmware files are
not easy to find right now. It's like, if you have a problem, tech
support will email the files to you.
For initial setup of an XW system, the "computer adapter method" is much
easier than the "buttons on the SCP method". The computer interface box
says Xanbus Diagnostic Tool on it; I presume there are some
troubleshooting routines in the software, but I haven't gotten that far.
All in all, I'm very happy to have this widget in my bag of tricks. The
adapter does have a wall cube which requires a small bit of 120 volt AC
power to operate, so that could be a challenge in some situations.
I have a client who will soon "field replace" the AC board in his XW
inverter, so not all board replacements in the field are prohibited. My
client toasted his relays by wiring the AC out from inverter #3
backwards to the other two. Messy, messy, but this is in no way the
fault of Xantrex. Now that we have two hots in each box we mustn't mix
them up.
Client, retailer, and manufacturer all suffered some brain damage and
tense times before the problem was discovered. Kudos to Mike @ Xantrex
for figuring this out!
Mick Abraham, Proprietor
www.abrahamsolar.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list