DC to AC Conversions Calcs.... [RE-wrenches]
Sky Sims
sky at ecologicalsystems.biz
Thu Jun 12 13:40:01 EDT 2008
I would interpret it based on the inverters name plate AC rating. So if
you used 3 SMA 7000's and 1 sma 4000 they would equal a combined
maximum AC output of 25kw. As for the exact amount of DC power going to
all of the inverters that would depend on the panels used. But assuming
you fully loaded the 7000's that would be 8400 watts per 7000 inverter
for a total of 25,200 DC watts to the 7000's + a fully loaded sma 4000
with 5100 watts gives you a total of 30,300 dc watts.
Sky Sims
Ecological Systems
http://www.ecologicalsystems.biz
220 County Road 522
Manalapan, NJ 07726
732-462-3858 toll free)866-759-7652 fax)732-462-3962
-----Original Message-----
From: Kirpal Khalsa [mailto:solarworks at gmail.com]
Sent: Wednesday, June 11, 2008 11:31 PM
To: RE-wrenches at topica.com
Subject: DC to AC Conversions Calcs.... [RE-wrenches]
Hi All......In Oregon the license for non electrician solar installers
is a LRT license.......This license is valid when working on a
permitted system up to 25kW AC.......What calculations might you all
use when determining the AC size of the system.........besides the
obvious.....Inverter efficiency losses de-rating and wiring losses
de-rating? I am trying to determine what the maximum size in terms
of a DC system would be able to be installed and not exceed the 25kW
AC system cap.....How might you all interpret that?
Thanks.....
--
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer TM
Renewable Energy Systems
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list