XW6048 running a 1HP pump? [RE-wrenches]

Ray Walters walters at taosnet.com
Mon Jun 9 12:51:09 EDT 2008


<x-flowed>

We had an older 1 Hp pump that ran on an SW4024, but NOT on a Outback  
VFX3624.
Funny, because I've run 3 HP pumps on a pair of Outbacks.
So this particular 1 Hp pump surged to over 5000 watts but less than  
7000 (according to the inverter ratings)
THis pump had some issues, but you need to have enough head room to  
handle the pump as it ages.
We fixed this one with a Franklin constant pressure controller that  
acts like the Grundfos SQE (No surge, pump varies rpm to always match  
flow to constant pressure)
It can work with any regular submersible AC pump.
I haven't tried the XW 6048, but it sounds like a monster. I'm pretty  
sure it should handle it,
and if not you switch the controller out. You don't have to pull the  
pump or change the plumbing.

Ray Walters

On Jun 9, 2008, at 9:04 AM, Chris Daum wrote:

>
> Warren:
>
> I have this 'application single phase motor chart' that says a  
> 240VAC pump
> has a maximum single phase load of 1600 watts continuous, and  
> locked rotor
> amps at 41.8....  I have found using this for worst case scenerios has
> covered my derriere in terms of being conservative in load  
> evaluation.   I
> hate to 'guess' that this new inverter would handle this load (I am  
> cautious
> about promoting new equipment!).  It SHOULD handle the 1 HP load,  
> but I
> don't want to offer it til I know.
>
> I do have a call in to Xantrex tech support, but have yet to hear  
> from then.
> I'll let you know what they say.
>
>
> Chris Daum
> Oasis Montana Inc.
> 406-777-4309
>
>
>
> -----Original Message-----
> From: Warren Lauzon [mailto:windsun at wind-sun.com]
> Sent: Monday, June 09, 2008 7:40 AM
> To: RE-wrenches at topica.com
> Subject: Re: XW6048 running a 1HP pump? [RE-wrenches]
>
>
> That seems a bit high, even for an AC pump. 1 HP is equal to 746  
> watts (not
> a true direct conversion, but close enough). So even if surge is 4x  
> that,
> would 3000 watts/VA
>
>


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------

</x-flowed>


More information about the RE-Wrenches mailing list