Apollo T-80 Alert [RE-wrenches]

Blair May tump at hughes.net
Fri May 9 09:44:50 EDT 2008


I too have found this product marginal in living up to expectations & in
need of revisions! Another "lets put it in the field & let the
installers tell us what we need to fix." Can you say vapor ware???? 
It seems every week there is a software update....hummm just 200
milesR/t to the unit, I'll get right on that.

-----Original Message-----
From: Mick Abraham [mailto:mick at abrahamsolar.com] 
Sent: Friday, May 09, 2008 9:38 AM
To: RE-wrenches at topica.com
Subject: Apollo T-80 Alert [RE-wrenches]



Hi, Wrenches~

The Apollo T-80 requires PV strings with more than 36 cells for every 12

volts of battery. I learned this while replacing a Trace C-40 control on

a 24 volt battery with "classic" array wiring (72 cells in each PV 
string). (The array is 20 feet in the air and there were no funds to pay

for an array re-configuration.) 

The Apollo unit would not work in this situation, and it took awhile to 
figure out why. I finally installed a Xantrex XW-MPPT controller, and it

does work. Apollo's instruction book calls for at least 32 volts peak 
power in order to charge a 24 volt battery. In additional  testing at my

own la-bor-a-tree, however, an array providing 35 to 38 volts peak power

(in the cool morning) still couldn't drive normal operation with a 24 
volt battery. The "35 to 38" volt number came off the XW controller 
display, which again tested fine after the T-80 balked.

I have suggested to Apollo that the spec in their instruction book may 
need revision, and I've also asked for better disclosure of this 
characteristic on all Apollo sales information. Weeks later, I'm still 
waiting for a response. Apollo did upgrade the hardware on this early 
vintage controller at no charge and they updated the firmware, but then 
they stopped answering my emails.

The T-80 may be a fine controller, but it is unsuitable for retrofit 
unless the array can be rewired with higher voltage strings. Apollo 
seems to find this unimportant; one of their techs even said that all 
MPPT type controllers have the same issue. 

Let's see: Outback, Blue Sky, BZ Products, and now Morningstar MPPT and 
Phocos...all have peak tracking type controllers which can directly 
replace a C-40 without changing the array...isn't that right? Apollo 
needs to disclose this factor more fully, and ignore emails from a 
concerned installer less fully.

Mick Abraham, Proprietor
www.abrahamsolar.com

P.S. If any of you would like to buy this demo controller, send me an 
offer off list. I don't have the carton and the left side knockout has 
been hammered out, but other than that it's in mint condition with a 
blank warranty card.


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-Wrenches mailing list